in our sub station why we step down firstly 33kv\11kv then
11kv to 430v. can we direct step down 33v to 430.v.
Answers were Sorted based on User's Feedback
Answer / gurucharan singh
Yes 100% you can directly step down from 33KV to 0.430KV.
You must take care transformer sizing should be as per LV
switchgear available at your end.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mandeep kumar
Yes it is possible to step down from33/.433kv But it can only depend upon the transformer turn ratio its ht turn will be in large nos than 11/.433kv.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anas
cuz u have to pass it first on substation (distribution
boards) to make it easier cut and start the current in case
of any fault happened and if u didnt do that damage we will
be easy not just easy very very very easy and cause the
transmission stations to damage and u will loss power when
u transform from 33kv to 430v directly ahuge amount of
current will be in the cable that means very huge cable
besides loads alaways
unbalanced..................................................
..................
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / ravinder
the rule of step down trf. 33kv\11kv step down in subsation
and get the one-by- one outgoing feeder's .
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / amit
FROM AMIT -SOHAM ELECTROWELL (P) LTD NASIK----WELL IF UR
LOAD IS ABOVE 1.5 MVA THEN THERE IS CHANCE OF fluctuation
ON 11KV~433 SO ITS BETTER U SHOUD GO FOR 33KV ~433V
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / devesh mishra
yes we can directly step down from 33/.433kv.
the lv side remains constant for 11 or 33kv & hv side
depends on load i.e,
for load upto 1.5 mva 11kv ht line is required,whereas
for load above 1.5 mva 33kv ht line is required
Is This Answer Correct ? | 3 Yes | 12 No |
sir i ve applied for hindustan petroleum and power grid india ltd..and the exams on feb 22.can you pls send model papers and tell how to prepare for those.i need to get into any of these for sure.....
why the stator is not laminated in DC machines?
why the projects getting loss?
An input device is interfaced with Intel 8085A microprocessor as memory mapped I/O.The address of the device is 2500H.In order to input data from the device to accumulator,the sequence of instruction will be
Which one hurts more AC or DC Current ?
what are the range of memory address in plc for L&T lx7 4A
How to calculate meter constant in HT yard pls give me example for this issue
1 Answers Juniper Networks, MacLellan,
why write 500v on line tester (Test pen)
why neutral is neccessary?
transmisancy eficencey calculation formula
IN star -delta motors normally first operated in star mode {absulated given (r-y-b) phases after one miute change in delta mode in this case i am change phase sequience for example R -PHASE TO CHANGE Y-PHASE ;Y-PHASE TO CHANGE R-PHASE SO THIS TIME MOTOR WILL HAPPEN RUNNIG MODE EIGHTER(OR) STOP MODE(TRIP MODE)
what the purpose of transmited high voltage in over head lines