in our sub station why we step down firstly 33kv\11kv then
11kv to 430v. can we direct step down 33v to 430.v.
Answers were Sorted based on User's Feedback
Answer / prateek lau
yes it is possible to step down 33kv directly to 430v but
in that the turn ratio of the transformer would be large
and it will increase the size as well as cost of the
transformer.
| Is This Answer Correct ? | 29 Yes | 6 No |
Answer / devesh mishra
yes we can directly step down from 33/.433kv.
the lv side remains constant for 11 or 33kv & hv side
depends on load i.e,
for load upto 4 mva 11kv ht line is required,whereas
for load above 4 mva 33kv ht line is required.
| Is This Answer Correct ? | 40 Yes | 25 No |
Answer / cv raman
Genarally load centers are very away from the Generating
stations & scattered too.No of 11/.430KV SS are very high
compared to 33/11KV SS. In the view of construction cost of
the 33/11KV SS is high compared to the 11/.430KV SS. At
this condition , construction cost of 33/0.420KV is very
high compared to the cost of 33/11KV SS. If we propose
33/0.420KV SS in all load centers the no. of ss will become
very high and construction cost will be very high.
Technically we can go for strigh step doun but it is not
economical.
| Is This Answer Correct ? | 16 Yes | 4 No |
yes we can do it.
But it is not feasible since
1]feeder were design on constant current (44kV/11Kv-line
from nearest substation to distribution transformer)
2]Distributor lines designs for constant voltage(11kV/440V-
line from distribution transformer to home)
It is normal practise to have less flctuation at load end.
please revert back for any query?
Nilkanth--SIEMENS
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / paramesh dutta
Yes, it can be done and it is being done. There are many
such substations with voltage ratio of 33kV/0.433kV.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / gurucharan singh
because of LV circuit breaker current capacity limitation
upto 3 MVA. Can directly step down from any voltage level
to 415V. but 3 MVA only that around 3150 A in Aluminium Bus
bar or 4000A in cu. bus bar. that about 3.5 MVA.
| Is This Answer Correct ? | 12 Yes | 9 No |
Answer / anuj
Yes we can step-down the voltage directly from 33kV to 430V
but it is not feasible since transformers turns will
increase which will ultimatly increases the cost and
secondly laod centres are far more distance than the S/S
which will increase the LT line and eventually the losses
are more in LT line than the HT line.Therefore from S/S to
the load centres, HT lines are running and near the load
centre distribution transformer is installed.By this way we
can reduce the LT line and ultimatly the losses
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ramesh
Generally we can step up high voltage to low
or low voltage to high voltage for a possible range.
which is balance for our economical stage
but technically it is possible the turn ratio of the
transformer would be large and it will increase the size as
well also differs cost of the transformer.
so that generation for 11 kv increases up-to level ll 750kv
11kv-33kv-66kv--132kv---400kv--750kv
step down as 11kv-440V- 230V-110V
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / bk
Technically it is possible to step down voltage level to
430V directly from any upper voltage level. However, our
power system network is connected to local power plant (may
be a CPP) that generates power at 11KV level. therefore it
is requred bring the network power voltage level to 11KV
for distribution purpose.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / vrs rathore
Yes we can, but if our exixting system is workable for only
11kv and required capacity is more then 4000kva then we
have to take 33kv connection and after that it has to step
down 11kv for supplying our esisting system, which is
working only for 11kv/430v.
| Is This Answer Correct ? | 3 Yes | 2 No |
How will u calculate wire size according to current rating?
How can claculate to attain the desired PF in the line ( HOW Much KVAR is required ) Pls Give the formula? Equate Petrochemical 0 1 how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec. 0 1 What will happened. if we feed 3phase supplay to the stater with out insert the rotor. How much current will flow through the stater winnding? Equate Petrochemical 0 1 What is required of exietation to the alternater. 0 1 why star point of HT motor not earthed? Equate Petrochemical 0 1 Why we are getting low voltage in star connection? Equate Petrochemical 0 2 What's ND relay & it's functions? Equate Petrochemical 0 2 How instantanious short circuit current is calculated? its formula? Equate Petrochemical 0 2 What is servo Motor? What's the advantages of this motor over Induction motor? Equate Petrochemical 0 2 What is core CT & it's function? Equate Petrochemical 0 3 what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY L & T 0 4 What is required of exietation to the alternater. KNB 1 23 what is the design voltage for 6.6KV 2000 KVAR HT capacitor? Consultancy 0 3 Pls explain about vfd control?Where it is used, Give some example? siemens 1 22 Please explain me abt PQ diagaram in the power sector. 0 9
in soft starter system for 375 KW 3 ph induction motor for multi stage vertical pump, two thyristers failed causing shorting of thyrister. the motor winding failed while starting.What is the cause and what is the effect in above case
I have 1500/1A CT If i connect this CT in 6.6KV bus bar means what will be the voltage present in CT?
sir, is there any ratio,this much of A.C volt is equal to D.C voltage
if the power factor is .88 i want to increase the power factor to .99 what number of capacitor is to add?
what is a relay?
Why indicate only 440V to 3-phase supply.
After doubling voltage from solar cells & use step down voltage transformer can we get high current output with low voltage.
What is the lower limit of break-down voltage of converter transformer.
How we can calculate the consumption in kwh of motor on basis of kw @100% load, @50% load & @ no load.
all types of electrical quations
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)