parallel operation for tansformer which condition fill fil
for that
Answers were Sorted based on User's Feedback
Answer / siddikh
1.polarity must be same
2.phase sequence must be same
3.turns transformation ratio must be sane
4.frequency must be same
5.% Impedence must be same
6.Vector group should be identical
| Is This Answer Correct ? | 19 Yes | 1 No |
Answer / irfan
1.polarity must be same
2.phase sequence must be same
3.equal voltage
| Is This Answer Correct ? | 11 Yes | 6 No |
1.polarity must be same ( Must be full fill )
2.phase sequence must be same (Must be full fill )
3.turns transformation ratio must be sane ( Desired )
4.frequency must be same ( Must be full Fill )
5.% Impedence must be same ( Desired as to ensure equall
load sharing of both the transformer
6.Vector group should be identical ( Desired )
| Is This Answer Correct ? | 6 Yes | 1 No |
following
1- KVA rating should be same
2- Voltage should be same and
3- frequency should be same
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manoj tyagi
1. same voltage ratio
2. the per unit leakage impedence of the xer r based on
their own kva rating must be equal
3. ratio of eqv. leakage reactance to eqv. resitance should
be same for all the xers
4.transformer must be connected properly
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / ashok
1)polarity will be same.
2)phase sequence must be same.
3) turns ratio will be same.
4)impedance will be same.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vilas
1)Transformer primery voltage rating should be same.
2)phase sequence should be same .
3)polarity should be same.
4) Vector group should be same ,for example :dy11 etc.
These point to be considered while making parallel
operation of the tansformer.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / maneswar
1.polarity must be same
2.phase sequence must be same
3.turns transformation ratio must be sane
4.frequency must be same
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / khalander mulla
to manage load at integrated steel plant to recover plant
load
| Is This Answer Correct ? | 0 Yes | 4 No |
How to calculate the current of Highpressure Mercury Vapour Lamp?what is the basis?whether we have to consider power factor or not?
What Should be the rating of transformer used in 33KV substation?
When VFD is connected to a 3 phase main supply there is load current difference between incomer to VFD and outgoing from VFD.
difference b/w series¶llel
What is real time power factor control panel(RTPFC)?
what is XLPE cable?
What is Class and accuracy in CTs? Types of Classes and important of Classes?
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.
Briefly describe your ideal job?
what is the contact resistance of sf6 circuit breaker??
This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????
howmuch current can carry the 2.5Sqmm copper cable?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)