when we r using 3.5 cable for a bldg. and put laod on each
phase using the neutral and neutral is the return paht for
the phase so the current of the neutral must be Ir+Ib+iY
(return).But the size of the netural is .5 as comper to the
phase.
Answers were Sorted based on User's Feedback
Answer / k.p.sharma
IN 3PH. NEUTRAL CARRIES ONLY UNBALANCE CURRENT MEANS IF ALL
PHASE ARE CARRYING SAME FOR EXAMPLE 20AMPS THEN CURRENT IN
NEUTRAL WILL BE ALMOST ZERO AMPS.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / saireen
3.5 c cable neutral is not the return path for the face but only that current which r unbalance among 3 phase, and that is sufficient to keep size 1\2 as compare to phase.
| Is This Answer Correct ? | 0 Yes | 0 No |
how to determine motor size for a fan application?
What are series and parallel isolators?
I have a shop heater with a 1/3 hp capacitor start, induction motor driving the fan. Intermittently, the fan motor speeds up significantly for several seconds (15-60 sec) then slows to normal operating speed. The manufacturer suggested changing the capacitor which made no sense, but I did it to no avail. Could this possibly be caused by the centrifugal switch intermittently reconnecting the start winding?
Capacitor bank require for 1000amp load
2 Answers Biodeal, Pharmaceutical,
Can we use the 60 HZ transformer/rectifier/Motors/Coils in 50 HZ? if not so, why?
they transformer oil leakeage to beather tank and top parts . they protection relayes was not operated.what is the oil leakeage problem.
Hi Suppose we have a wye/wye transformer which is grounded at both sides,in this situation, do we have ay ground transformer? in other words, ground transformer can do any thing more (while we have nuetral wire in both sides)? As the last question, what about 3rd harmonic? we have two choices: first using wye/delta transformer + ground transformer and second using wye/wye earthed connection.in the former choice, we dont have 3rd harmoonic at the secondary side but what about Yn/yn conection? do we suffer from 3rd harmonic in the Yn/yn connection?
Why different types of connection in transformers are used? (star/star,star/delta,delta/star,delta/delta)Why we are only taking in consideration of star/delta type transformers? if only star/delta is good in practice where doses other type of transformers are used? Note: i want to know place of using different types of transformers other than Star/delta type with brief description.
What is difference b/w Microwave and OPGW ??
Expand sqcm?
which of the following motors is non-self starting?
What are the effects of electrical faults?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)