When VFD is connected to a 3 phase main supply there is
load current difference between incomer to VFD and outgoing
from VFD.
Answer / pinak
sir,first tell me by what instrument you are measuring the
current,probably clamp meter.the thing is like that in case
of VFD's the incoming frequency is not same as the outgoing
frequency.so due to this change in frequency the current do
changes. sir i hope if you just supply 50Hz on incomming
siode and from the output you are also taking 50 Hz then
the current doesnot changes.
| Is This Answer Correct ? | 9 Yes | 5 No |
whatis the test procedure for lightning arrester which was installed one year back. i want check it whether it is working or not.
Why grables are put in substation?
what is current overloading in stack
what are cable earthing and bus earthing trucks?when and where they are used?
How can we do megger test of cable??
WHAT IS THE FUNCTION OF SHORT CIRCUIT MAINTENANCE CT
ups and invertor battery selection chart and full formula
in dc shunt generator field is open in running condition what will happen?
what is the difference between effective earthing and resistive earthing?
wat is the difference between rotor 1st stage fault and 2nd stage fault?
what are the applications of transistors with low dc gain, high dc gain and medium dc gain( beta)?
define frequency ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)