Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


This is about the recent problem that we have faced in our
project site.
We have 6/7.5 MVA. 66/11kV three phase star - star power
transformer. The neutral was solidly connected to the
earthing mat. But because of high resistance of earthing
mat (130 ohm on LV and 180 ohm on HV), one day LV side
neutral earthing conductor melted and we had a huge damage.

Can any one plz tell me what might happen when we connect
power transformer neutral to the earthing mat which has
high resistance (>100 ohm ) ?????

Answers were Sorted based on User's Feedback



This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/1..

Answer / k.prakashchandra

Have you measured IR properly, as the values are very high
?The IR should not exceed 2 ohms for a 66 KV MUSS .I do not
know whether primary neutral is to be earthed in case of
star/star tr.It is stated that LV side IR is 130 ohms ,and
hence the maximum earth fault current will be 50A.For 7.5
MVA tr the rated LV line current is about 400 A and EFR is
likely to be set at 80A.It appears that the earth wire
melted due to continuous earth fault current.If there is
conductor to ground fault at a distance of 100 m from tr
earthing ,there will be a pd of 63.5 V /m along the line
between the fault point and the neutral earth. If anybody
stands barefooted with feet 1 m apart along this line, he is
likely to be electrocuted as the power line does not
trip.Further the ground around the earthing also may be at
nearly phase voltage during earth fault

Is This Answer Correct ?    1 Yes 0 No

This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/1..

Answer / gairhe

I think you are right.

for the LV even if the imbalance neutral current is 10 A,
the 130 ohm resistance will produce GPR ( Ground Potential
Rise ) of 10 X 130 = 1.3 kV.

Also at the site the transformer neutral earth conductor was
touching the 185 sq mm single core copper power cable and
control cable. May be because of this high GPR , sparking
occurred and heat was generated.

The neutral earthing conductor is of size 95 sq mm. so 10 A
current is not a big issue.

In my view 1.3 kV and sparking developed heating at the
group of XLPE power cable, control cable and fire started .
Then the XLPE power cable was damaged and because of the hig
earth fault from the damage of XLPE cable, the near by
neutral earthing conductor got melted.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

WHAT HAPPEN IF LT SUPPLY 415 V FED TO THE HT 3.3KV MOTOR

1 Answers  


why square root 2 is multiplied with line voltage in selection of LA ie 11/sqrtroot3=6.35 kv and it is multiplied with sqrt2 ie 6.35 KV*sqrt2=8.9 kv we will select 9kv.my question is why we are multiplying with sqrt 2?

1 Answers   KSPL,


voltage at generation stage is usually- ? a.11kv b.33kv c.66kv d.220kv

12 Answers  


How to operate a ac chilar plant?

0 Answers  


11KV electrical line going through the forest in cloudy night ,how can we find the direction of line.

5 Answers   Bhel, Cesco, HZL, Nesco,


1.how many earth pits are required for 1000 k.w plant include substion , transformer ? 2. how many earth pits are required for 500kva generator.what is formula to calcute?

0 Answers  


On a 3 winding transformer YNynd11, how do you apply REF protection to the Delta tertiary winding that is supplying auxiliaries to a substation?

0 Answers   Kwekwe Polytechnic,


Explain what is use of lockout relay in ht voltage?

0 Answers  


in star connected 4wired transmission system ,what happen if the neutral is grounded . or not grounded. which is significant and y

2 Answers  


1.WHAT IS A SMART CAPABLE DB ( DISTRIBUTION BOX) ? 2. HOW TO DECIDE THE TYPE OF DB TO BE USED ( RECESSED/ PLUG TYPE/ SMART ETC ETC? 3. WHAT IS MILLENEUM BUS BAR USED IN DB? 4.DIFFERENTIATE MCCB AND MCB.

0 Answers  


what are the available sizes of pin type terminal lugs in the market today?

0 Answers  


what is the ground fault relay,which purpose it will be use,clearly tell me plz

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)