what is mean of 3 by 2 automation ?
Answers were Sorted based on User's Feedback
Answer / farooq
if three sensors installed to measure or monitor one process
variable and when two of them give a high or equal to a set
value than an alarm or correcting action can be activated is
called 2 out of 3 automtion.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / senthil
for example,consider the three transmitters are in
service.in logic,the three xtr compare each other value i.e
A&B,B&C,C&A. check the diff of deviation b/w the
comparison.the xtrs showing minimum deviation is taken,from
this the mean is taken b/w two xtrs.this is 2 0f 3.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / ladla
this information is apply for alarm and trip system where
these shows the redundant of the system
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / senthil
2 out of 3:
for example:
we use three pressure transmitters in the process line
discharge of a pump.consider the range is ( 0 to 10 bar).we
have a condition that when the discharge pressure is low the
pump has to trip(less than 4bar).
-if two transmitters goes below this value there is trip.
we have deviation alarm,deviation deadband warning also in 2
voting 3 concept.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gopi
step by step implimentation our logics by using any controller
| Is This Answer Correct ? | 0 Yes | 1 No |
what is reset windup in integral control?
What for barriers are used in DCS & PLC systems?
when the operation engineer told you that he gives the control valve order to open but there is no response ! what will you do ? and if you found that there is astuck , what will you do ? (note : it is apanumatic valve )
what is the difference between Feedback controller and Feed forward controller. and when it is to be used.
If any control valve create hunting problem, what is the possible reason and solution?
How to Calibrate the magnetic flow meter on site ?
whatis diference between zero pressure and obsolute pressure
What is close loop ?
1 Answers College School Exams Tests, GMR,
How can test or measure the probe and extension cable to identify if the problem at the probe or cable or at the driver it self? (pleast notify the measuring method)
what is lead lag compensator and for wat v using that???
Reason for capillary type dp level transmitter fluctuation
why we are using orfice plate? then difference between orfice 7 nozzle plate?
1 Answers Flour Tech Engineers (P) Ltd,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)