how we calculate the 30 KW 3phase electric motor current on
noload

Answers were Sorted based on User's Feedback



how we calculate the 30 KW 3phase electric motor current on noload..

Answer / j.kesavan

30 KW MOTOR NOMALLY FULL LOAD 54 AMPS, BUT WITH OUT LOAD
30% CURRENT WILL TAKE,ANY THREE PHASE INDUCTION MOTOR WITH
OUT LOAD 30PERSENT CURRENT WILL TAKE.

Is This Answer Correct ?    257 Yes 60 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / d.g.skandan

No load current of a 3phase induction motor varies
according to its KW and rpm. Normally as a thumb rule
fraction HP motors (below 2.2KW) will be 50% of full load
current. Above 2.2KW may be 20% to 30% OF full load
current.

Is This Answer Correct ?    92 Yes 23 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / mahmoud

In=p/1.732*v*p.f

=30x1000/1.732*.8*380

=57A

Ino=57/3
19A

Is This Answer Correct ?    108 Yes 46 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / suresh

no standerd farmulla to calculate the noload current but as
a thumbrule 3 ph induction motor will draw 30% current on
no load but few motor will take 50 to 60 % current

Is This Answer Correct ?    65 Yes 16 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / suthan prabhu

Actually,there is no standard formula to calculate the
noload current of the motor.Normally 25% to 40% of full
load current of the motor.Also depending upon motor KW and
supplier..

Is This Answer Correct ?    54 Yes 11 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / vikram

P = 30 kw
V= 415
I = ?
PF =0.8
p= 1.732 VI PF

I = 30000/1.732*415*0.8

I= 52.17 Amp (Full load current)

No load current will be 30% of FL current

N.L Current = 30% * 52.17

NLC = 15.65 A (Without taking Efficiency of motor into account)

Is This Answer Correct ?    43 Yes 2 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / surajkant

practically the no load current of 3 phase motor varies
from 25% to 35% whereas in 1phase it is nera to full laod.

Is This Answer Correct ?    28 Yes 15 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / s.p.singh

There is no standerd formula for calculating no load
current, It depend on the desine and material used in
motor. There is a major role of material(winding wire&
stamoing)to anhancing the efficiancy of motor.

Is This Answer Correct ?    14 Yes 3 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / pillay

I agree with suthan prabu. there is no formula to calculate.
depends on the manufacturers design, but full load curret can be calculated.

Is This Answer Correct ?    22 Yes 12 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / k.arivazhagan

3 ph induction motor will run 30% current on
no load but few motor will take 40% current


EXAMPLE:

KW=3.7KW,Amps=7.45,(Assume 40% Of No Load Amps)

No Load Amps = 7.45*0.4
= 2.98A

Is This Answer Correct ?    15 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

WHAT IS MEANT BY DERATING OF THYRISTOR?

0 Answers   TATA, Trane,


What difference between ref protection and differential protection ?

0 Answers   EPC, INEL Power System Engineers,


Determine the BTU size of an aircon for 20 sq metre room

0 Answers  


What is full form of ELECTRICAL?

3 Answers   Changwoon, DP World, Electrical, GSS, HCL, ITI, L&T, Maruti Suzuki, MCC, SMR, Somany Ceramics, TRDP, Wipro,


What are applications of Shunt release?

2 Answers   Techno Electric and Engineering,






What the formula for calculating no.of earthings & size of earth strip for 100mX90m shop.

0 Answers  


how tubelight circuit is connected and how it works?

7 Answers   Punj Lloyd Ltd,


when the rheostat kept in minimum to maximum position in motors what will happen?

7 Answers  


I want to measure resistance between Neutro and earth conductor for 3 phase Transformer what should i do

1 Answers  


what is the most probable reason of failure of current transformer?

2 Answers   L&T,


what are the reasons of low voltage during start the DG?

1 Answers   Godrej, Tata Power,


what is the difference SCR & TRIAC?

13 Answers   TCS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)