how we calculate the 30 KW 3phase electric motor current on
noload
Answers were Sorted based on User's Feedback
Answer / j.kesavan
30 KW MOTOR NOMALLY FULL LOAD 54 AMPS, BUT WITH OUT LOAD
30% CURRENT WILL TAKE,ANY THREE PHASE INDUCTION MOTOR WITH
OUT LOAD 30PERSENT CURRENT WILL TAKE.
| Is This Answer Correct ? | 258 Yes | 60 No |
Answer / d.g.skandan
No load current of a 3phase induction motor varies
according to its KW and rpm. Normally as a thumb rule
fraction HP motors (below 2.2KW) will be 50% of full load
current. Above 2.2KW may be 20% to 30% OF full load
current.
| Is This Answer Correct ? | 92 Yes | 23 No |
Answer / mahmoud
In=p/1.732*v*p.f
=30x1000/1.732*.8*380
=57A
Ino=57/3
19A
| Is This Answer Correct ? | 108 Yes | 46 No |
Answer / suresh
no standerd farmulla to calculate the noload current but as
a thumbrule 3 ph induction motor will draw 30% current on
no load but few motor will take 50 to 60 % current
| Is This Answer Correct ? | 65 Yes | 16 No |
Answer / suthan prabhu
Actually,there is no standard formula to calculate the
noload current of the motor.Normally 25% to 40% of full
load current of the motor.Also depending upon motor KW and
supplier..
| Is This Answer Correct ? | 54 Yes | 11 No |
Answer / vikram
P = 30 kw
V= 415
I = ?
PF =0.8
p= 1.732 VI PF
I = 30000/1.732*415*0.8
I= 52.17 Amp (Full load current)
No load current will be 30% of FL current
N.L Current = 30% * 52.17
NLC = 15.65 A (Without taking Efficiency of motor into account)
| Is This Answer Correct ? | 43 Yes | 2 No |
Answer / surajkant
practically the no load current of 3 phase motor varies
from 25% to 35% whereas in 1phase it is nera to full laod.
| Is This Answer Correct ? | 28 Yes | 15 No |
Answer / s.p.singh
There is no standerd formula for calculating no load
current, It depend on the desine and material used in
motor. There is a major role of material(winding wire&
stamoing)to anhancing the efficiancy of motor.
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / k.arivazhagan
3 ph induction motor will run 30% current on
no load but few motor will take 40% current
EXAMPLE:
KW=3.7KW,Amps=7.45,(Assume 40% Of No Load Amps)
No Load Amps = 7.45*0.4
= 2.98A
| Is This Answer Correct ? | 15 Yes | 6 No |
TRANSFORMERS WITH DC SUPPLY
How to make vector group test of transformer?
Why can't we parallel Voltage transformer secondary circuits?
To test Transformer we give HT side 440V to see wheather that it is producing 17.6V on LT to verify Voltage ratio is correct or not but when we give the 440V voltage to LT side then what will happen to HT voltage ?
what is the pre charge circuit,what will be work which function it will be use plz tell me
what is the use of sdf?
What is the difference between an ELCB and a RCD?
what is the voltage between the earth & neutral 2 is there any continuity TO BE between earth & NEUTRAL
I am experienced with house and industrial wiring but I don't have any licence how can I apply an licence and which type of licence i can get i didn't complete deee just only experience
Is only insulation the difference between High voltage and Medium voltage cable?
Y phase plates are used in transmission line??? what is there need???
How to calculate % Impedence?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)