how we calculate the 30 KW 3phase electric motor current on
noload
Answers were Sorted based on User's Feedback
Answer / j.kesavan
30 KW MOTOR NOMALLY FULL LOAD 54 AMPS, BUT WITH OUT LOAD
30% CURRENT WILL TAKE,ANY THREE PHASE INDUCTION MOTOR WITH
OUT LOAD 30PERSENT CURRENT WILL TAKE.
Is This Answer Correct ? | 257 Yes | 60 No |
Answer / d.g.skandan
No load current of a 3phase induction motor varies
according to its KW and rpm. Normally as a thumb rule
fraction HP motors (below 2.2KW) will be 50% of full load
current. Above 2.2KW may be 20% to 30% OF full load
current.
Is This Answer Correct ? | 92 Yes | 23 No |
Answer / mahmoud
In=p/1.732*v*p.f
=30x1000/1.732*.8*380
=57A
Ino=57/3
19A
Is This Answer Correct ? | 108 Yes | 46 No |
Answer / suresh
no standerd farmulla to calculate the noload current but as
a thumbrule 3 ph induction motor will draw 30% current on
no load but few motor will take 50 to 60 % current
Is This Answer Correct ? | 65 Yes | 16 No |
Answer / suthan prabhu
Actually,there is no standard formula to calculate the
noload current of the motor.Normally 25% to 40% of full
load current of the motor.Also depending upon motor KW and
supplier..
Is This Answer Correct ? | 54 Yes | 11 No |
Answer / vikram
P = 30 kw
V= 415
I = ?
PF =0.8
p= 1.732 VI PF
I = 30000/1.732*415*0.8
I= 52.17 Amp (Full load current)
No load current will be 30% of FL current
N.L Current = 30% * 52.17
NLC = 15.65 A (Without taking Efficiency of motor into account)
Is This Answer Correct ? | 43 Yes | 2 No |
Answer / surajkant
practically the no load current of 3 phase motor varies
from 25% to 35% whereas in 1phase it is nera to full laod.
Is This Answer Correct ? | 28 Yes | 15 No |
Answer / s.p.singh
There is no standerd formula for calculating no load
current, It depend on the desine and material used in
motor. There is a major role of material(winding wire&
stamoing)to anhancing the efficiancy of motor.
Is This Answer Correct ? | 14 Yes | 3 No |
Answer / k.arivazhagan
3 ph induction motor will run 30% current on
no load but few motor will take 40% current
EXAMPLE:
KW=3.7KW,Amps=7.45,(Assume 40% Of No Load Amps)
No Load Amps = 7.45*0.4
= 2.98A
Is This Answer Correct ? | 15 Yes | 6 No |
WHAT IS MEANT BY DERATING OF THYRISTOR?
What difference between ref protection and differential protection ?
0 Answers EPC, INEL Power System Engineers,
Determine the BTU size of an aircon for 20 sq metre room
What is full form of ELECTRICAL?
3 Answers Changwoon, DP World, Electrical, GSS, HCL, ITI, L&T, Maruti Suzuki, MCC, SMR, Somany Ceramics, TRDP, Wipro,
What are applications of Shunt release?
2 Answers Techno Electric and Engineering,
What the formula for calculating no.of earthings & size of earth strip for 100mX90m shop.
how tubelight circuit is connected and how it works?
when the rheostat kept in minimum to maximum position in motors what will happen?
I want to measure resistance between Neutro and earth conductor for 3 phase Transformer what should i do
what is the most probable reason of failure of current transformer?
what are the reasons of low voltage during start the DG?
what is the difference SCR & TRIAC?