why is the rating of transformer done in kva and not in kw.
Answers were Sorted based on User's Feedback
Answer / manthesh.patil
transformer is rated in kva bcoz cu losses are dependent on
current and iron losses are dependent on voltage ,& they are
independent on powerfactor so transformer is rated in kva
not in kw
| Is This Answer Correct ? | 39 Yes | 5 No |
Answer / lakshmanan m
According to my opinion, manufacturer cant design the
particular transformer for specific load (capacitive or
inductive load) Thats why they dont give the power in KW.
Because KW= vxIx power factor. but power factor is
depending upon the load. So commonly they are give the KVA
power only. It means KVA= Vx I only. According to the load
we can calculate the KW rating.
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / manoj-essar
dear manoj, there is no concern of static or rotating
device, then why r u saying in this way?
Trafo is not having unity pf but it depends upon load type
of trafo...(inductive or capacitive or resistive load)
| Is This Answer Correct ? | 17 Yes | 6 No |
Answer / sachin /vaibhav
as core loss depends upon voltage & copper loss on
current independant of PF. HENCE RATING IS IN KVA
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / vasumalai madhavan
In transfomer, the core loss depends upon voltage and
copperloss depends on current , it was (transoformer) not
dependable on power factor . thats why the rating of the
transformer always in kva not in kw....
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / shinyvikram ganji
rating of the transformer is done based on losses(core and
copper losses).
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / ravi
transformer losses are in terms of current and voltage only
i.e (I Square R) copper loss and VI is the Core loss. i.e y
units are in KVA
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / beau
because transformer capacity takes care of both real power
consumed by resistive loads and reactive power in inductive
and capacitive loads such as motors and the transformer's
windings inductive reactance(Apparent power KVA).
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / thiyagarajan
kv is an apparent power kw is an active power the ratio
between active and apparent power is power factor ,we dont
know the power factor before connecting to load that why we
are used to refer kv in transmission
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the basic principle of operating of a television camera tube?
in cable joints procedure what electrical problems have been solved out ?
why we not use capcitor in Three phase motor ??
2 Answers GOMS, Power Electronics,
What is diversity factor in electric installations?
All the voltage drops and the source voltage added together in a series circuit is equal to
What is Skin effect in Cable?
what is consequences of neutral and earth connect?
how hydrogen or helium is a cooling agent for alternator./ generator of big size.
Can we calculate the P.F if we know the only load on alternator .
what happen if the supply is given to the stator of the 3phase induction motor with out assembling the rotor ?
How much current flow in no load condition of a motor?
In a incandescent bulb, if the glass is punctured, and then power is supplied, the tungsten filament blows up with a flash.Why?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)