TO operate transformers in parallel, vector symbol of the
both should be same.If one transformer name plate is not
there, how can we conclude that whether the transformer is
having the same vector symbol or not?
Answers were Sorted based on User's Feedback
Answer / guru
Check the vector group by carrying out VECTOR Group testing
( By Injecting a 3 Ph 440v or 230 V to the primary windings
and check the voltage between the terminals in secondary
side)
For each vector group there are standard values which has
to come in the secondary side
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajendran
we can easily find out and confirm the vector group of the
transformer by using the standard test procedures.
| Is This Answer Correct ? | 3 Yes | 3 No |
This vector group test is done at site to check if their is
any damage in the windings during transportation and
erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted.
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
| Is This Answer Correct ? | 0 Yes | 0 No |
single phase voltage 230 and Three phase voltage 450 why 690 voltage
what are the tests comes under the type test, what tests comes under routine tests.
Iam deepthi.i completed my b.tech from electrical engineering.i want to prepare for civil services.i dont have much knowledge about these exams,but i have great zeal of cracking exams.plz provide me suggestions to which options i can select for optionals
what happend when 230v dc motor we supplied a 23v ac supply
in three pin pluge there three pins one is phase and second is earth third is nutral why nutral high diameter compare with phase and earth
why transformer is conneted to dc for polarity test.it doesnt work in dc?
1)which height building required lightning arrester? 2)how to calculate the requirement of lightning arrester? 3)what is the pro instrument? 5)how to test protective relay like overload?earth fault relay?
what is the maximum rating(KVA) of transformer can be used in distribution side..(11KV/440v) and why??
If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor rating accordingly.Illustrate by showing formula?
what is potentiometer & rheostat
size of condotory fron voltage level
what is the sweep commenly used 1200mm sweep and 600mmsweep please tell me breifly sweep
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)