TO operate transformers in parallel, vector symbol of the
both should be same.If one transformer name plate is not
there, how can we conclude that whether the transformer is
having the same vector symbol or not?
Answers were Sorted based on User's Feedback
Answer / guru
Check the vector group by carrying out VECTOR Group testing
( By Injecting a 3 Ph 440v or 230 V to the primary windings
and check the voltage between the terminals in secondary
side)
For each vector group there are standard values which has
to come in the secondary side
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajendran
we can easily find out and confirm the vector group of the
transformer by using the standard test procedures.
Is This Answer Correct ? | 3 Yes | 3 No |
This vector group test is done at site to check if their is
any damage in the windings during transportation and
erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted.
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
Is This Answer Correct ? | 0 Yes | 0 No |
low voltage distribution is done by a)3 phase 3 wire b)3 phase 4 wire c)single phase
explain types of electric welding and its applications
Please explain how to do 'tan-delta test' on AC generator? and where i get clear and brief detail, give any web page address.
in case of three phase induction motor,when it is connected to three phase supply,why the magnetic field is rotets around the armeture?
If 440 V supply has given at the secondary winding of transformer at that time if we apply 11 KV at primery then what will happen???????
what is Different between Bilinear and Unilenier?
What is the name of process In VFD frequency are increase then voltage increase & frequency decrease then voltage decrease?
WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?
identify the components of the tube light and explain how they function???wat is inside the fluroscent tube???how it works???
What must be the minimum distance maintained between 2 Generators as per International standards?
is it ok to switch lights from a mcb instead of switches
what are the basic insulation levels & what its Unit