wat is the difference between rotor 1st stage fault and 2nd
stage fault?
Answers were Sorted based on User's Feedback
Answer / shamshad ansari
First stage fault only alarm and second stage trip the generator.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shamshad
First stage only alarm and second stage trip the generator.
| Is This Answer Correct ? | 0 Yes | 0 No |
Hi friend i m glad dat u came up with a question like dat .
i appreciate ur indepth study of power system .
well basically the rotor system of altenators are unearthed
due to which the single gound fault at the rotor doesnt
actually disturbs the rotor as there is no fault current ,
however if a second gorund to earth faukt develops then the
short circuit between the windings results as the fault
current gets a path to flow . the former is called the 1st
stage fault while the latter is called the 2nd stage fault.
| Is This Answer Correct ? | 0 Yes | 1 No |
Why are tertiary windings used in transformers?
( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK Answer # 1 The capacitor current would be kvar x 1000 / (415 x sqrt3). This would be 70a approx. The MCCB selected should have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So you should choose at least 100 A mccb.) regarding to this answer,i would like to know why the current have to times 1.4 to get the right amphere for the mccb.hows the formula to get the 1.4??tq
how we calculate size of exciter(excit. volt and current) for generator?
Why don't connect earth wire to elcb?if earth fault occur,how will detect it
1 Answers TATA, Tata Communications, Telecommunications,
what should be the BDV value Of 11/132kv power transformer
What are HT & LT Cables? What are their values?
howmany insolaters needed in 66kv line
Wt is the function of reactive power? How it generates & consume though resultant is zero?
What are the factor to be consider for CT selection in 132kV substation?
What happens when generator is running with leading power factor on it say -0.96. what are the effects of it on alternator and the other generators operating in parallel to it.
what is LOS(line of sight)?
How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
1 Answers Ajanta Pharma, Bhel, Cosmo Films, Suzlon,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)