why the capacitors works on ac only
Answers were Sorted based on User's Feedback
Answer / bala
generally capacitor gives infinite resistance to dc
components(i.e., block the dc components). it allows the ac
components to pass through.
Is This Answer Correct ? | 33 Yes | 2 No |
Reactance of capacitor X = 1/(2πfc)
Since f=0, for dc frequency is zero.
So, Reactance X will be infinity for dc.
means capacitor blocks dc and allows only ac to pass
Is This Answer Correct ? | 17 Yes | 0 No |
Answer / yuvi
Both capacitors and inductors are reactive components and
can be used only with AC circuits.
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / rakesh
Only high frequency
allowed to pass
through the capacitor,
& dc supply has
0(zero) frequency due
to this reason
capacitor work on only
ac.
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / krunal devi
for a capacitor in case of DC source applied over it first half of its period it goes on charging but it is not getting time for discharge because for DC source the current is constant . That's why it is working as break in dc circuit.
Is This Answer Correct ? | 3 Yes | 1 No |
is that any software calculator to calculate the size of cable
can we say current flows inside an atom as electron moves inside an atom?
in 11kv generators the neutral point is connected to earth via earth coil while in the 33 / 11 kv transformer the neutral point is connected to earth via earth resistor why?
hi can you give any body fault level calculation, generator fault level calculation,transformer fault level calculation for system fault level with equation? i have 3.3kv generation voltage three gas gen sets, one is 1.9MW,2nd is 2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one gas gen sets is 3.8MW, we are step up to 22kv by transformer
3 Answers Hindalco, Piramal Healthcare,
Can we use BS 6651 and BS EN 62305 standards for computer room lightning ptotection in substation?
why in generating station generation voltage is 11 kv
What shocks us , Current or voltage?
what is percentage impedance of transformer? explain its significance
what is the function of RVT
What are the special protection given for high capacity Motor, more then 10mw
what will be happen if we apply D.C supply to the transformer
We have a 33/11kv switchyard having 12.5 MVA power transformer. We export & import power through this transformer. When we export power, the PF will be depend on GRID PF & when we import power the PF will be depend on our load PF. but the problem is that,when neither we export nor import but our 33KV vCB is in close position,our meter read the power factor 0.14 to 0.25 at that moment. So how can be we improve the power factor at that moment.