How the Transformer oil testing is done & Why oil dielectric
goes LOW & what is solution for that ??
Answers were Sorted based on User's Feedback
The sample oil to be tested for dielectric test is collected
and put into the tester and the average of 6 tests is
taken.The minimum withold voltage is as per local regulations.
causes of low dielectric results are usually exposure of the
insulating oil to moisture through the breather or there is an
exposed opening, poor quality oil being used. high acidic
content.The insulating oil should be replaced or dehydrated.
breathers silica gels should be maintained good all the time
and check for any leaks or any exposure to atmosphere must be
rectified.
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / ravikumar.g
The transformer Oil testing to be done in filtration unit
by checking the Oil Testing Kit in KV
20 KV low
when the voltage are not balancing properly and the taps
are changing regurly the oil becomes carbonsied this
carbonsied oil is acts as conductor.
So these problem so we change the Oil.
The salution for this changing the oil the transformer has
to be oilfilteration in once in a year.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / saroj
TRF oil is tested in a glass pot where high voltage,KV is
applied between two electrodes and sparking at electrode to
be observed. For good oil , it comes about 40~60KV/mm .If
it comes lower then filteration is required. Those TRF
having tap changing is frequently required it is
recommended to do filteration in once in year.Also its
value goes low because of moisture ingress in oil .
| Is This Answer Correct ? | 5 Yes | 1 No |
using n1*n2 which type transformer is made; where n1 is primary turn and n2 is secondery turn
Which of the following alternatives will be cheaper (1) A 100 h.p AC, 3-phase motor (2) Four motors of 25 h.p each (3) Five motors of 20 h.p each (4) 10 motors of 10 h.p each explain
In a 11000/440 V transformer, when any one phase of 11 KV supply fails (ie., single phasing), what happens to the secondary voltage and why?
3 Answers Secure Meters, TCS, Torrent Power,
tate and explain super position theorem
How the speed of synchronous motor changes with the variation of load?
why single phase induction motors are not self staring ? how can we start the 1-phase Induction motor ?
WHY EARTHING NOT NEEDED IN BATTERY IN SUBSTATION?
what is electricial and mechnical interlock.
9 Answers Control Dynamics, EFS, HP,
what is meant by vector group of a transformer? How can it be derived?
what parameters are should nessary for control technic dc drive(in rolling mills)?
how can we understand that where we have to use ac or dc coil for solenoid valve and why?what is the different between coil of ac and dc explain please.
what will happen if i connect or change line with phase terminal
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)