How the Transformer oil testing is done & Why oil dielectric
goes LOW & what is solution for that ??
Answers were Sorted based on User's Feedback
The sample oil to be tested for dielectric test is collected
and put into the tester and the average of 6 tests is
taken.The minimum withold voltage is as per local regulations.
causes of low dielectric results are usually exposure of the
insulating oil to moisture through the breather or there is an
exposed opening, poor quality oil being used. high acidic
content.The insulating oil should be replaced or dehydrated.
breathers silica gels should be maintained good all the time
and check for any leaks or any exposure to atmosphere must be
rectified.
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / ravikumar.g
The transformer Oil testing to be done in filtration unit
by checking the Oil Testing Kit in KV
20 KV low
when the voltage are not balancing properly and the taps
are changing regurly the oil becomes carbonsied this
carbonsied oil is acts as conductor.
So these problem so we change the Oil.
The salution for this changing the oil the transformer has
to be oilfilteration in once in a year.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / saroj
TRF oil is tested in a glass pot where high voltage,KV is
applied between two electrodes and sparking at electrode to
be observed. For good oil , it comes about 40~60KV/mm .If
it comes lower then filteration is required. Those TRF
having tap changing is frequently required it is
recommended to do filteration in once in year.Also its
value goes low because of moisture ingress in oil .
| Is This Answer Correct ? | 5 Yes | 1 No |
why series motor cannot be started on no-load?
WHAT IS THE SPECIFICATIONS CONSIDERED DURING DESIGN FOR THE OVER CURRENT RELAY?
what is breaking capacity
For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details.
Give the selection criteria of a 3 Phase transformer for industrial purposes ?
Could explain briefly of over excitation in transformer.
What is neutral earth voltage of transformer and what should be the value
Three phase power is measured with two wattmeeter for balance three phase load.the reading of one wattmeter is zero.we can conclude that the power factor of balance load is?
what is exiter winding,stator winding,avr?how it will work?
what is use of governer in diesle engine
How would you supply power to a village which is very far from a sub-station and has only a 11k?
What are difference between earthing switch and earthing truck ? What is the operation philoshopy of earthing truck ? Wht are the component of earthing truck ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)