110 KW MOTER DOL STATER 240SQ.MM CABLE MOTER AND STARTER
DISTANCE IS 110 METER WHAT IS VOTAGE IN MOTER END AND
SYSTEM VOTAGE IS 415 V HOW I CAN CALCULTE
Answers were Sorted based on User's Feedback
Answer / capseee
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / m s rana
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
But it is not engineering to run 110kw motor run to DOL
Starter It IS VERY HIGH LOAD & LONG DISTANCE higher losses
Is This Answer Correct ? | 2 Yes | 4 No |
how to calculate the lightning arrester conductor @ no of earth pits required
how to calculate singlephase motor efficiency?
What are the necessary solutions needed to be carried out on a malfunctioned earthing mechanism of a VACUUM CIRCUIT BREAKER.(TAMCO)
back emf of motor at the time of starting ?
Based on what the rating of machines are provided??(ANswer should in single word)
19 Answers Asian Paints, Bhel,
what is difference between electrical and electronics
What will be the voltage impact on secondary side of two transformers with different vector groups when both voltages are compared.
what is circuit recombiner and how it is different from circuit breaker
If 24 KVA AVR having Input voltage 200-400v, Output voltage 415+-1%, what will be the voltage if Load is 13A.
lenz law application and define
What are the tests to be conducted in the electrical installations
What is NGR . What is the purpose of 10 sec ,60 sec rating of NGR.