We have a 62.5 KVA DG with Leyland engine and kirloskar
slipring alternator. We have earthed the neutral, and another
earthing for the dg body. is it necessary to isolate the dg
foundation with rubber pads?
As your DG is a small capacity,it is okFor large DG ,dg
founations are earthed. rubber pads reduce the vibrations.
Is This Answer Correct ? | 2 Yes | 0 No |
Explain the function and difference of Restricted earth fault, simple earth fault and sensitive earth fault with connection diagram.
How do u term the word 'OF' in Megger Testing???
what is the difference between synchronous & asynchronous generators
what is the working process of over & under voltage relay.
hi, could someone help me to find a control design for syncronising panel .
What is meant by short-pitched winding?
After taking shutdown of 11kv feeder, if you see 5kv by phasing stick in the cable side, is it possible to close earth switch in cable.
SIR, GIVE ME OPGW SAG CALCULATION FORMULA I AM DAE ELECTRICAL. THANKS
how to calculate the phase diffrence beetween given two equetion y= 15sin(wt+pi/3) and y=10sin(wt-pi/4)
A 11KV, 1200 A breaker combination fixed in a cubicle for HT motor.Is normally for 11 KV motor fuse is using? if Yes, What range fuse is required?
i have one source transformer with the capacity of 50KVA, connected with two loads 10kw and second one is 15kw.. how can i calculate first load in KVA and second one in KVA .. because Kva rating, power factor rating of of transformer is different from the load… there must be some way to calculate load KVA rating and power factor….