Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Should transformer earthing pit, to be connect to earthing
mat in Substation

Answers were Sorted based on User's Feedback



Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / niranjan

ยท The system earthing and safety earthing are interconnected and therefore fault current flowing through system ground raises the potential of the safety ground and also causes steep potential gradient in and around the Substation. But separating the two earthing systems have disadvantages like higher short circuit current, low current flows through relays and long distance to be covered to separate the two earths. After weighing the merits and demerits in each case, the common practice of common and solid (direct) grounding system designed for effective earthing and safe potential gradients is being adopted.

Is This Answer Correct ?    3 Yes 0 No

Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / siva kumar

during fault conditions the fault current fed from transformer neutral.So the earth pit which is connected to neutral has to supply fault current.
supplying of quantity of fault current by earth pit has limitations such as soil type.CIPipe lengh etc.
if you connect neutral earth pit to substation mat, the mat will supply the fault current.

it is just like earth as big water reservoir and water as current. If more and more parlel pipe lines are laid more quantity of water can be dischrged quickly.

Is This Answer Correct ?    1 Yes 0 No

Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / pankaj agarwal

as the short circuit fault devlops in the system the fault
current flows from fault point into the neutral. in the
absense of interconnection, all the fault current has to
travel through ground which have high resistivity so the EF
current flowing in the system may not be sufficient to
operate the EF trip relay. in the interconnected system EF
current have alternate and less resistive path so fault
gets cleared fast.

Is This Answer Correct ?    1 Yes 0 No

Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / nipesh

but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), in this case transformer body earthing and substation earthing both are joint through metal gland, is this safe for transformer and other equipment?

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What happen if field ckt is open when a sailent pole alternator connected to infinite bus

3 Answers   Bhel, Nilkamal,


In induction machine when the load increase the current will increase .why? what is the relation ship between the sleep and current drown by stater?

1 Answers  


IN 6.6KV 3 phase switch gear .i will give 6.6kv to R phase only to earth in during H.v testing (through H.v KIT).what happen remaining phases.how much voltage get remaining phases.why? explain.

1 Answers  


What is Surge arrest? How it work?

4 Answers  


what is meaning of bus raiser???

1 Answers  


what is diff. between earthing grid,earthing mess, earting grid?

0 Answers   Century Rayon, Emco, Tailor Solution,


Please help me.What are the difference between two wire, 3wire, and 4 wire in electric meter?

3 Answers  


what is the type of pilot wire in pilot relay?

1 Answers  


Explain about Leakage Test.

0 Answers  


what is consequences of neutral and earth connect?

0 Answers  


Brief use of isolation transformer & how it works.

1 Answers  


i am BSEE student, my project study is to synchronize the generator of an hospital, it have a one 313KVA standby-power diesel gen.,and three 100kva transformer.The generator system is operated manually and no ATS or UPS. one more new building is being build so the transformer will be upgrade to a higher vale. 1)how i can connect the new gen. to the old gen. and to the synchronize panel? 2)what is the new gen. to be buy?(rating, etc.) These is my title: To synchronize the generator system of the ____ Hospital. Anyone have a good title? Thanks.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)