Answer / niranjan
ยท The system earthing and safety earthing are interconnected and therefore fault current flowing through system ground raises the potential of the safety ground and also causes steep potential gradient in and around the Substation. But separating the two earthing systems have disadvantages like higher short circuit current, low current flows through relays and long distance to be covered to separate the two earths. After weighing the merits and demerits in each case, the common practice of common and solid (direct) grounding system designed for effective earthing and safe potential gradients is being adopted.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / siva kumar
during fault conditions the fault current fed from transformer neutral.So the earth pit which is connected to neutral has to supply fault current.
supplying of quantity of fault current by earth pit has limitations such as soil type.CIPipe lengh etc.
if you connect neutral earth pit to substation mat, the mat will supply the fault current.
it is just like earth as big water reservoir and water as current. If more and more parlel pipe lines are laid more quantity of water can be dischrged quickly.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pankaj agarwal
as the short circuit fault devlops in the system the fault
current flows from fault point into the neutral. in the
absense of interconnection, all the fault current has to
travel through ground which have high resistivity so the EF
current flowing in the system may not be sufficient to
operate the EF trip relay. in the interconnected system EF
current have alternate and less resistive path so fault
gets cleared fast.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nipesh
but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), in this case transformer body earthing and substation earthing both are joint through metal gland, is this safe for transformer and other equipment?
| Is This Answer Correct ? | 1 Yes | 0 No |
I have an enquiry of develop solar power plant, 0.69/11kV, 1500kV/750/750kVA, Dy11y11 Transformer. I want to know what does 1500kV/750/750kVA means? Sorry if this is a noob question.
If not maintained 3 phase clearance,what happened ?
Both generator parallel condition shared load equally but one genrator taking ampere more than the other what are all the causes to make like this
can induction motor becomes as a generator. if yes how it is possible. if there is a squirrel cage rotor.
What do you mean by 4.44 in this transformer equetion E=4.44 nfqm
Is ground earthing required for neutral conductor of a prime mover ie DG set?
determine two methods to find loose connection in operational electrical system?
wht is this amps in power consuption and how can we convert that into consuption hours ? i am a sales executive of a energy saving lamps .
in transformer input is d.c signal which type of emf is induced
whenewher three phase supply is given to induction motors revolving/rotating field is created & rotor rotates.When the three phase supply is given to three phase transformer then revolving,/rotating field is created or not? if not why?
Find the octal equivalent for the binary number 101101110
How will you explain transformer action in case of 3-phase induction motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)