Answer / niranjan
ยท The system earthing and safety earthing are interconnected and therefore fault current flowing through system ground raises the potential of the safety ground and also causes steep potential gradient in and around the Substation. But separating the two earthing systems have disadvantages like higher short circuit current, low current flows through relays and long distance to be covered to separate the two earths. After weighing the merits and demerits in each case, the common practice of common and solid (direct) grounding system designed for effective earthing and safe potential gradients is being adopted.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / siva kumar
during fault conditions the fault current fed from transformer neutral.So the earth pit which is connected to neutral has to supply fault current.
supplying of quantity of fault current by earth pit has limitations such as soil type.CIPipe lengh etc.
if you connect neutral earth pit to substation mat, the mat will supply the fault current.
it is just like earth as big water reservoir and water as current. If more and more parlel pipe lines are laid more quantity of water can be dischrged quickly.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pankaj agarwal
as the short circuit fault devlops in the system the fault
current flows from fault point into the neutral. in the
absense of interconnection, all the fault current has to
travel through ground which have high resistivity so the EF
current flowing in the system may not be sufficient to
operate the EF trip relay. in the interconnected system EF
current have alternate and less resistive path so fault
gets cleared fast.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nipesh
but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), in this case transformer body earthing and substation earthing both are joint through metal gland, is this safe for transformer and other equipment?
Is This Answer Correct ? | 1 Yes | 0 No |
what is the difference between the diode and the rectifier
17 Answers Avalon, L&T, Mahacol Trexim,
what is meaning of bus riser
how to find the 2500 KVA transformer rated primary and secondary volt and current?
What is the effect of positive feedback on stability of the system?
what is reactive power?
How to calculate the FUSE rating?
Can be ammeter and voltmeter used without CT? if not, what is the reason for that?
3 Answers Elektrotek, Toyo Engineering,
what is Ith current?
What is difference between 3 point and 4 point starter
1 Answers Genco, Kaltec, TATA,
what is the difference between inductive load and capacitive load?give me some examples in general
Explain with example of functional requirements of protection relay in terms reliability, selectivity, sensitivity
what is the difference between star connected and delta connected motors