During he starting up of the motor, the upstream's MCCB
(350A) always trips due to the UVT relay activated.
Can Star-delta starter use for a 20kW Motor (For a powder
mixer machine) cause voltage-dip in the supply line voltage?
If so, what are the recommended solution to
eliminate/reduce the transient voltage dip in the line
voltage?
Answers were Sorted based on User's Feedback
Answer / tushar patil
yes u can use star delta starter
20KW means 30HP motor
u can use VFD (variable frequency drive) also
it is very easy to u
if cable length is more than 50 m then u should connect output line chock to output n input line also connect line chock..
n increase accelaration time in vfd
| Is This Answer Correct ? | 0 Yes | 0 No |
You can check the length of the cable from the supply to
motor, I think It will be more so that due to line
resistance loss during starting the line voltage will go
down for the fraction of seconds.
please mention the connected load, transformer capacity,
volatge incoming etc for further clear answer.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / abdulsubur
up to 3kw Dol startor
up to 7kw we can use Star delta startor
| Is This Answer Correct ? | 2 Yes | 3 No |
what is different between auto transformer and vriac
What are the rating wise protections required for Generators from 600KVA to 2000KVA
for preparation of design note of 11 / 220 kV , 3 phase, 63 MVA transformer how can calculate or consider the iron losses and copper losses
please forward me the type of questions which would rise while me attending to 33KV Electrical License to my mail ID:vadrevu_raghava@yahoo.co.in
how we calculate torque ? how we improve it ?where torque will either motor or generator ?
I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500A load.Can I connect this load directly to the Busbar since I have PROTECTION IN MY MDP Panel ?
Draw the wave shape of armature current in a generator subjected to a sudden three phase short- circuit at its terminals. Define various reactance of generator from this wave shape.
what is recovery voltage & transient voltage ?
How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99
4 Answers Dhanalakshmi Industries, DLF,
purpose of breaker contact multiplication relay?
I would like to install the largest KW alternator to a 200 amp aluminum bus box in my home. Is it possible to install a 250 KW 400v 251amp synchronous alternator to my home?
What should be cable size for 75KVA 380/220 3ph transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)