purpose of breaker contact multiplication relay?
Answers were Sorted based on User's Feedback
Generally manufacturer provide only 2NO+2NC Contacts.But
the client need more application such as remote
indications,interlocks,other switching operations photocell
camera,DCS,.....which need more contacts to represent CB
conditions. this is done with multiplication relay.
| Is This Answer Correct ? | 18 Yes | 4 No |
Answer / rajesh
the purpose of breaker contact multiplication relay is to
get NO & NC contacts, which can be used for breaker on and
off indication in remote places.
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / sourav pramanik
contact multiplication relay are used for incresing contact...let there are so many on off switch ,alarm are to be activated..but main relay contacts are very less..so to increase contact we use cmr.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / rbkrishnan
And there are three coil A,B,C are used in that .my
question is what are the coil pickups during breaker on &
off
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / rohantamhane
A,B,C, coil in the breaker one coil is closing coil and two
coil for tripping coil for Back up proteaction
| Is This Answer Correct ? | 2 Yes | 4 No |
static chagre
How to connect the chemical earthing and complete process tell me plz
How can transformer oil be used in transformers with voltage rating above its breakdown voltage?
i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.
What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?
To prevent the mal operation of a differentially connected relay while energizing a transformer, the relay restraining coil is baised with (a)second harmonic current (b)fifth harmonic current (c)third harmonic current (d)seventh harmonic current
why do we use 3 single phase instead of one 3 phase?? though vee connection is its advantage but what is the hidden reason behind it??
How CT & PT ratings are decided for a 11KV or 33KV transmission line?
In 1000KVA Transformer why does we connect HT with delta connection and LT with star connection.Illustrate by showing formula?
why some time Railway Fan not Rotate,But after a small rotation by human then it rotate normally? Why?
Why electricity is generated and transmitted at the values of multiples of 11?
How can we decide the fualt levels of sub-stations?
2 Answers Bhel, Enercon, Prakash Industries,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)