Answer / shashi
P=1.732VI
SO P=75KVA(75000 VA)
V=220 V
I=236
Considering safety you can lay aluminum cable of 240 sqmm or 95 sqmm copper cable
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raja
4c x 50mm² Armoured Cable + 1c x 25mm² Earth Cable
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / essemmay
thanx raja..is it possible 50mm2 for both side cables..incomer and outgoing of the transformer, since the incomer voltage is 380 and outgoing is 220, so the same size is enough??
Is This Answer Correct ? | 0 Yes | 2 No |