How much KVAr bank reqired for 630 KVA transformer on full
load for maintain power factor upto.99
Answers were Sorted based on User's Feedback
Capacitor calculation is depends on load. if 630 KVA transformer is loaded fully with load p.f.=1 then no compansation is required but if the same is fully loaded with load p.f. = 0.8 then, kvar required is calculated as below:
KVAR = KW ( tanǾ1-tanǾ2); Ǿ1=old p.f.angle, Ǿ2=new pf angle
= 504 ( 0.75 - 0.14) [ here, KW=504 because, 630 X 0.8 = 504]
= 307.44 KVAR
say, 300 KVAR bank is required at load end for compansation
Is This Answer Correct ? | 15 Yes | 4 No |
Answer / engr junaid afrid
Simply says 630/2=315 kvar for your system.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mahendra singh
KVAR = KVA * sin@
KVAR = KVA * sqrt (1-cos@*cos@)
KVAR = 630* sqrt(1-.99*.99)
KVAR = 88.87
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / sanjay
generally kvar depends upon 33% of full load. please suggest if i m wrong.
Is This Answer Correct ? | 0 Yes | 2 No |
What is the difference between Contactor and Circuit breaker ?
what is the sweep commenly used 1200mm sweep and 600mmsweep please tell me breifly sweep
What is the starting current of a DC Motor?
what is the applicatyons of the slipring motor and please tel me more about the slipring concept
what is the use of cable in our environment ?
Can anybody just suggest about the scope of Electrical design with ETAP software?Just guide me?
what are the differenc between vcb and sf6 breakers
How we can test the Smoke Detectors????
What is burden of a current transformer. What is function of core in Transformer
1 Answers Jindal Steel and Power, NCC,
Why we oil in tranformer/
how much earthings are provided for 22KV HT Metering Kiosk
1 Answers GE, Gionee, Knight Frank, TATA, Vacmet,
give me the details of anti pumping relay