How much KVAr bank reqired for 630 KVA transformer on full
load for maintain power factor upto.99
Answers were Sorted based on User's Feedback
Capacitor calculation is depends on load. if 630 KVA transformer is loaded fully with load p.f.=1 then no compansation is required but if the same is fully loaded with load p.f. = 0.8 then, kvar required is calculated as below:
KVAR = KW ( tanǾ1-tanǾ2); Ǿ1=old p.f.angle, Ǿ2=new pf angle
= 504 ( 0.75 - 0.14) [ here, KW=504 because, 630 X 0.8 = 504]
= 307.44 KVAR
say, 300 KVAR bank is required at load end for compansation
| Is This Answer Correct ? | 15 Yes | 4 No |
Answer / engr junaid afrid
Simply says 630/2=315 kvar for your system.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mahendra singh
KVAR = KVA * sin@
KVAR = KVA * sqrt (1-cos@*cos@)
KVAR = 630* sqrt(1-.99*.99)
KVAR = 88.87
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / sanjay
generally kvar depends upon 33% of full load. please suggest if i m wrong.
| Is This Answer Correct ? | 0 Yes | 2 No |
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
How do we measure earth fault current in Generator Transformer(20/420kv),Station Transformer(20/11 kv) and Unit Transformers(20/11kv) for our plant system, since these don't have any Neutral earth Fault relay connected to their Neutral Earth? But for Unit Service transformers(11/.433 Kv) we have an Earth Fault Relay connected to its neutral earth.Why is such so?
why reactive power control is required
What is d main advantage of using double circuit 3 phase transmission ?
How stabilizer works??
Differentiate between digital phase converter and ordinary phase converter.
i have gear oil pump with single phase motor.some time its motor starts running in reverse direction rather than forward direction...whats the reason behind this issue. 1- either capacitor is week? 2- or winding is week?
why ct secondary side shortlink provided? its open what will happen?while running ?
what is transient stability analysis means?
What current flows in the transformer primary when its secondary is open?
previous year paper of ntpc bhel for degree in electrical enng
what is reactive power?, why its measured in VA ? is it transient behavior of system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)