for preparation of design note of 11 / 220 kV , 3 phase,
63 MVA transformer how can calculate or consider the iron
losses and copper losses
Answer / aamod tripathi
The Iron and copper losses are determined by tests only. It
is guaranteed parameter. If not met . the manufacturer has
to be imposed with a penalty calculated according to the
life of the transformer.
However as a thumb rule. 63 MVA transformer will have 1 -
2.5 % of no load + copper losses.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the different ratings of ACB/VCB/SF6 which is used at HT side
I am getting differential earth fault in my transformer realy , i have checked all its CT & control wiring but do not get fault, Please help
what happen if turbine trip ,g.c.b not open and excitation on condition?
Why ferranti effect occurred in leading p.f load?
GIVE CONDITION FOR MAX EFFICIENCY OF 3-PH TRANSFORMER AND D.C MOTOR
What is meant by coupling capacitor?
I want to merge a cable..in between two metering Cubicals which contains CT's and PT's and Energy meter..before taking merger..what are the common things required?
Why power factor does not occur in DG set ?
purpose of check value
Logic using 1 kV or 1,1 kV grade in house wiring Low voltage cable. Explain/suggest? some use 1kV and some prefer 1.1kV grade insulation low voltage cable why??
What is the different between Earthing & grounding?
what is meant by peak load
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)