I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel
with 4000A Breaker.Already I have 2500A load.Can I connect
this load directly to the Busbar since I have PROTECTION IN
MY MDP Panel ?
Answers were Sorted based on User's Feedback
Answer / jagadisha.n bmsit
ya we can..
Actual rating of the motor is 4000A and it was carrying
2500A load since if we connect 500A tio same busbar it
becomes 3000A so it can handled both the load but the prob
is if fault occured in 1 line both the line will trip..
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / santosh bangar
no , because it will trip 2500 A load if fault occur at MDP
it is possible if MDP have it's breaker to clear fault.
then you can connect to MCC bus
Is This Answer Correct ? | 0 Yes | 0 No |
Dear friend.
Mathamatically it looks possible but bofore making this
arrangment the other factor which you need to consider.
1. The Rating of a transformer.
2. the Ir seeting of a Breaker.
3. Total contract demand if you are using local electricity
board power.
4. change in OT & WT setting.
by checking all the above peramiters you can go ahead.
Is This Answer Correct ? | 0 Yes | 1 No |
what is the working principle of ceiling fan and table fan?
10 Answers ABC, Tata Steel Limited,
LT, CC and LMU installed at both the outgoing circuits of 132 kv double ckt transmissio what its means ? and what are there use ?
what is the total power generation in india?
what is the use of megger? and types
11 Answers TNEB Tamil Nadu Electricity Board,
Can anybody tell me what the breakdown voltage is for air and what it is for transformer oil please?
What is ST and specify its range of voltage.
Why grounding is generally done in supply end?
i need the details about bhel exam.how to apply for that.please send to my email-id.thenmozhi2k7@gmail.com
what is the difference between droop mode and ischnorous mode in thermal powerplant?
What is the significance of 3.5 core cable ????
8 Answers Intelux Electronics,
why we use the fuse in only one wire? althrough in ac current the current flows in both directions. why the neutral wire can be taken half the magnitude of phase wire while same current returns from neutral wire?
Why is negative feedback invariably preferred in closed loop system?