I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel
with 4000A Breaker.Already I have 2500A load.Can I connect
this load directly to the Busbar since I have PROTECTION IN
MY MDP Panel ?
Answers were Sorted based on User's Feedback
Answer / jagadisha.n bmsit
ya we can..
Actual rating of the motor is 4000A and it was carrying
2500A load since if we connect 500A tio same busbar it
becomes 3000A so it can handled both the load but the prob
is if fault occured in 1 line both the line will trip..
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / santosh bangar
no , because it will trip 2500 A load if fault occur at MDP
it is possible if MDP have it's breaker to clear fault.
then you can connect to MCC bus
| Is This Answer Correct ? | 0 Yes | 0 No |
Dear friend.
Mathamatically it looks possible but bofore making this
arrangment the other factor which you need to consider.
1. The Rating of a transformer.
2. the Ir seeting of a Breaker.
3. Total contract demand if you are using local electricity
board power.
4. change in OT & WT setting.
by checking all the above peramiters you can go ahead.
| Is This Answer Correct ? | 0 Yes | 1 No |
Why are the voltage levels in a powersystem are 11KV,33KV etc., why not 10KV,30KV?
Name quantities which are not transformed in the tranformer.
what happen if the load connected to the induction motor is taken away? the same question for synchoronous generator in synch i think that the the exitation voltage will appear on the terminal only if so plz answer me
what is the difference between ground and neutral?
which electrical supply used for long distance traction 1.1-ph 22kv a.c 50hz 2.2-ph 22kv a.c 50 hz 3.dc vtg 4.1-ph 22kv 150 jhz
why capacitor is placed in fan
difference between the applicability of nortons and thevenin theorem
What are Directly Exited Generators?
can we individually produce electriciyt
What happen if in three phase 440 v , when you check voltage by testor it glows except one phase and in the same time when you check by multimeter it shows 440 v in any two phase.what will be the reason...
What do you mean by ratio correction factor of instrument transformer?
Why carbon brushes are used in motors?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)