How we check vector group for a Dyn1 transformer?
Answers were Sorted based on User's Feedback
Answer / s.ravindra
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / gunasekaran
we can find out from ratio kit
if applied UV-vn get energised
if applied VW-wn get energised
if applied WU-un get energised
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / vinod maurya
We will short 1U & 2U
And we will apply 3 phase voltage between 1U,1V,1W
Measure between
1U-1V
1V-1W
1W-1U
1V-2v
1V-2w
1W-2w
1W-2v
1W-2n
2n-1U
Verify The Condition
1W-2n+2n-1U= 1U-1W
1W-2w=1W-2v
1V-2v<1V-2w
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / y.rama krishna
Connect 1U&2U
Apply 3ph 415V balanced voltage across terminals 1U,1V,1W
(HV wdg)
Measure the voltages between the given terminals & record
1)1U-1V
2)1V-1W
3)1W-1V
4)1V-2V
5)1V-2W
6)1W-2V
7)1W-2W
8)1U-2N
9)1V-2N
Verify the conditions
a)1W-2W = 1W-2V
b)1V-2W = 1V-2V
c)1U-1V = (1U-2N)+(1V-2N)
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 18 Yes | 16 No |
Answer / mahmoud moustafa
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
this is correct I check today in one of GE sites
| Is This Answer Correct ? | 2 Yes | 0 No |
number of I/O devices in siemense plc
what is working of no & nc.
hi i have a 400kva transformer i want to know the test i can use to check on it thx
What is a copper loss or i2r loss pc?
What is the specification of service line (ie from electrical post to cut out) used by electricity boards used in india.i mean which material,its size etc.. please give the answer at lalkishan.p@gmail.com
diffrence between alternating and pulsating field?
Why increase in current leads to increase in conductor temperature?
230v 1 phase Phase and Neutral insert in Bulk water what happens.
how to increase senstivity of ct
What is the calculation for 1000Amps Air circuit breaker relay settings.
What is the advantangeous over SFU (switch fuse Unit) & FsU (Fuse Switch unit) which one is better & application of Both?
how to set the overload setting in the thermal overload relay?? is there any calculation in that??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)