how to set the overload setting in the thermal overload
relay?? is there any calculation in that??
Answers were Sorted based on User's Feedback
Answer / elango k
it is based on the charaterstic of olr
100% to flc can be set it is normal
85% to flc can be set it is sharp
because an olr starts to work 115% of flc
for eg. if a motors flc is 100 amps
i am setting 85amps , the olr starts to work
at 100amps it trips the motor
Is This Answer Correct ? | 13 Yes | 6 No |
Answer / balasubramaniyan.t
Overload setting in the thermal overload relay to be done based on the motor full load current.The setting current of the relay should not exceed the motor FLC.
Is This Answer Correct ? | 12 Yes | 7 No |
Answer / veerendra
the overload relay setting is donr based on the value of
line current of the motor..
first calculate the line current & set the elay for the same..
Is This Answer Correct ? | 4 Yes | 9 No |
What is the Procedure for selecting a Cable, Breaker and Transformer for particular load.
what is the difference between underreach and overreach.what is the advantage of using overreach instead of underreach.explain
why solinoid coil used in tripping rely?and why not other type coil?
how to connect the three phase capacitor in three phase star/delta connection motor?
what will happen if neutal in AC ckt will get open
What happen while we measure the Current in Rotor?
how did the testing of protection relays done through current injection
give me a clear defination of inductance,and how can u calculate inductance of a motor
In case of generator when we consume more power produces by it why load on generator increase and starts sound more. and how it is adjusted..
How many types of probe used in cro?
Earth has zero potential then what would be the neutral potential ?
what are the deffects for failure of PLC?