Pls say , how we calculate lux / sq.ft, which formula used
for calculation
Answers were Sorted based on User's Feedback
Answer / krishna pathak
To Calculate the no. of fittings in a room,
the formula is
N=No. of Light fittings required= A x E/(Lxuxd.f)
.'. E= N x (Lxuxd.f)/A
where L=> Lumen o/p
A=> Area (m^2)
E=> Illumination or Lux levels (in lux)
u=> coefficient of utilization
d.f=> Depreciation Factor
For Detail study refer Philips,G.E(lighting)& Artlite
Catalogues.
| Is This Answer Correct ? | 24 Yes | 9 No |
Answer / aarya
To Calculate the no. of fittings in a room,
the formula is
N=No. of Light fittings required= A x E/(Lxuxd.f)
.'. E= N x (Lxuxd.f)/A
where L=> Lumen o/p
A=> Area (m^2)
E=> Illumination or Lux levels (in lux)
u=> coefficient of utilization
d.f=> Depreciation Factor
For Detail study refer Philips,G.E(lighting)& Artlite
Catalogues.
| Is This Answer Correct ? | 18 Yes | 5 No |
Lux = Lumens/sq.ft.
for one are the formula will be -
Area in sq. mtrs X Required Lux
No. of fixtures = -------------------------------
Lumens O/p of fixture X U.F X D.F
Uday Kulkarni
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / chandrakant zingade
Per Sq.ft Lux = 1 x Total Lux / Total area in Sq.ft.
| Is This Answer Correct ? | 5 Yes | 5 No |
Importance of fault current in power transformers and how to monitor the same? How is it different from winding temperature?
What should be the earthing resistance of an industrial substation and also What should be the house hold earthing resistance?
20 Answers Jindal, Pharma, TAAT, TATA,
which motor is suitable for traction? why?
what is MC 61 relay
What is the function of Fuel and Oil filter in DG.
What is meant by Active and reactive power?
23 Answers College School Exams Tests, Schneider, Torrent Power,
What are the effects to a distribution transformer rated 10Kv with ratio 10Kv/0.433Kv, 3phase 50hz for example but fed with power supply of 11Kv?
What difference between TRANSFORMERS and TRANSDUCERS???
in single phase we get 220 volt and in three phase 4420 v why this second Ques= in case three phase star conection our neutrul becom disconect what happan 3 Q=== a three phase house load and have unbalce load on different pahse diffrent current eg phase a 7A b 8A c 5A and voltage is 440 than how calculate it total load in kw pl give formula thanks
why neutral can not used in three phase motor connection?
Dear Sir/Madam, I have one questions we have three steam turbines and one Gas turbine and our industry linked with the public network, we have protection system one of the protection is reverse power we can export just four MW only i would like to ask about how to calculate the reverse power. Thank you in advance best regards
a solar energy installation utilizes a three phase bridge converter to feed energy into power system through a transformer of 400v/400v.the energy is collected in a bank of 400v battery and is connected to converter through a large filter choke of resistance 10ohms.1.the maximum current through the battrey will be.2.the kva rating of the input transformer is.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)