Pls say , how we calculate lux / sq.ft, which formula used
for calculation
Answer Posted / sudheer
we can calculate lux level by lux meter.
Total lumens required= A . E . D/U where,
A = surface area(sq.m)
E= illumination(lm/sq.m)
D= dipriciation factor
U= co-efficient of utilization
| Is This Answer Correct ? | 38 Yes | 15 No |
Post New Answer View All Answers
Apparent power is expressed as V * I(Conjugate). Why not in V * I ?
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
how to calculate short circuit current for the busbar
What is the mechanism of WTI
How many types of losses occur in a transformer?
what will be happen if earth point is being used for as a neutral point for raw power , and same will be used for ups earthing
How will change the frequency in distribution side?
What is the minimum value of hfe for the oscillations in transistorized rc phase shift oscillator?
How to reduce -234126219.6403 MVAr generation and by what?
Explain Need of a starter in a dc motor.? Also explain any two starting and speed control method of dc motor?
What are the classifications of heating element?
what is through fault?
What it the purpose of parallel phasing transfomers??
how to identify vector group of three phase transformer by voltage method?
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?