give single line diagram of D.O.L and star -Delta starter ?
Answers were Sorted based on User's Feedback
Answer / rajesh.p
Dol starter means direct on line starter and its capacity
is below 5hp
Is This Answer Correct ? | 142 Yes | 19 No |
Answer / mafat
IT IS POSSIBLE TO DOL STARTER WILL BE CONVERTED TO
MICROPROSSER TYPE STARTER
Is This Answer Correct ? | 70 Yes | 18 No |
Answer / j.senthil kumar
D.O.L Starter:
Motor connected either via Contactor or directly from the
Three/Single Phase Lines.
Star delta Starter:
We require three contators for make the Star-delta
combination, The contactor looping are attached herewith
for your reference.
Is This Answer Correct ? | 37 Yes | 4 No |
Answer / hardik prajapati
1)Up To 7.5 HP - DOL Starter
industrial application one contactor are used
2)Up To 7.5 To 20 HP star Delta
Star Delta starter three Contactor Are used
and one Star/Delta Timer are Used
-- MCCB
-- Three Contactor
-- over Load Relay
-- Timer
-- SPP (Single Phase Priventer)
-- Control Fuse
Is This Answer Correct ? | 3 Yes | 0 No |
How the annunciator works ? How to do its wiring
If we have two nodes A and B and Vab is the potential difference between these nodes then which node is called reference node a.node A b.node B c. Ground node
If i am running of spindle at 2000rpm ,but How to spindle stop at the second I am resetting the machine in CNC machines
What is the meaning of EDO in DG panels?
How the speed of synchronous motor changes with the variation of load?
WHAT IS LOAD CELL
Why PT voltages are measured with respect to ground? What do u mean by voltage or current polarized.
In the ACB breaker capacity is 2000Amp but this each phase taken 1250 But total beldibg load is 600amp or 700amp watt is the problem
What does Magnetic Neutral Axis
2 Answers Eskom, Genus, Lanco,
Why a ballast and ignitor is required in MH and other lighting fixtures
How to calculate electrical Induction motor heating and cooling time constant,11KV,2850,12P,SCIM
minimu size and length of gi earth pipe