Answer / naresh pipaliya
by using starter, we can control starting current becus, at
the time of starting current is very high. It may damage
stator winding so we have to us starter to control starting
current.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / k.gowrishankar
At starting condition,heavy current will flows.to limit the
starting current we are using the starters.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / yogi
Starter means at the time of starting our motor takes more
current due to low emf in starting so its function is to
limit the starting current. we know in starting motor takes
5 to7 times current of rated current.
for starting induction motor we use three method which
are further giving
1.Direct on line starter.
2.AutoTransformer.
3.Star-Delta.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / arun mutharasu
starter give the reduced voltage,limited the starting current and starting torque
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / subhakanta sahu
As we know at the time of starting an induction motor the rotor is stand still hence the slip is 1.if slip is 1 the rotor induced voltage is maximum hence drives maximum current in the rotor circuit.This rotor current current has impact on stator current(As per LENZ's law).This is the reason why an induction motor takes high current at starting(About 5 to 7 times the full load current).
This high current causes voltage fluctuation,unwanted power loss & unwanted stress to the system or equipment.So it has to be reduced by using different starting methods.
There are two possible ways to limit the starting current
1.Reduce the applied voltage.
2.Increase the rotor resistance.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nitin mavi
the armature current of amotor is given by Ia=(V-E)/Ra.
thus Ia depends upon E & Ra,if V is kept constant. when a
motor 1st starts , the armature is stationary so the back
emf is 0 and Ra is very low so Ia is very large. this
current will spark in brushes, damage windings &
commutator. that's it.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / girish.r
R2 is D.Proportional to (1-s) { s = (Ns-N)/Ns) } . Same as
a transformer, Sy current determines the primery current.
So at starting R2=0 as ( N=0 and s=1). So Sy current is
very high as much as 5 times than F.L current. Hence as per
Transformer action py current also is so high. By reducing
the applied voltage or introducing resistance in the rotor
ckt this ckt interference can be reduced . FOR WHICH WE
USE A STARTER.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / saravanan.s.r.
Starter is mainly used inorder to reduce the HIGH STARTING
CURRENT and to protect the electrical equipments.at the
time of starting the slip=1;speed=less; hence the rotor
resistance value equals '0' due to the relation r2(1-s)/s.
there is no back emf,such that it draws a high starting
current.It may lead to damage the equipments in motor.hence
to avoid this starter is used.main types of starters are
1.Direct On Line starter.
2.Auto Transformer starter.
3.Rotor Resistance starter.
4.Star - Delta starter.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pravin patil
To limit the starting current of an induction motor starter are used.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dhaval
1) The rotor of the three phase induction motor is act as a short circuit secondary while the stator winding is act as a primary winding of transformer.
2) Due to this, short circuited secondary, the current flowing through primary winding increases upto its 5 to 7 times the rated current for a few seconds.
3) Due to the increase in current, I2R losses are takes place in stator winding which results in overheating.
4) Similarly, it also reduces supply voltage at the time of starting.
5) Hence, in order to avoid this problems, starter is necessity for starting of induction motor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Which standard i will refer for size of earthing conductor for equipment? (Eg:415V Switchgear, MCC, DB shall be 50x6mm GI flat)
Why DG set rating in KVA
Do you know what is dry-out test in x'mer
0 Answers First American Corporation, GPSC Gujarat Public Service Commission, Jindal,
Why the suply frequency in INDIA is 50HZ
How to calculate the load loss and no load losses of the power Transformer? i am having the following details : full load ct : in AMP HV :1676 ; LV:31.5 1800 KVA ;33KV/620 V for wind mill applications
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
how to identified power tranfer line is how much KV????
Define early construction of human being
in 3 phase (4 wire) star connection - is current pass through neutral??
WHAT HAPPENS IF FUSE IS CONNECTED TO NEUTRAL WIRE
why protection meter is always connect to star
What are all the points to be checked while decanting diesel from tanker lorry to HSD YARD
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)