Why is starter necessary for a three-phase induction motor?
Answers were Sorted based on User's Feedback
Answer / pramitha
A reduced voltage is applied at the starting,and the
voltage is increased to the rated value,when the motor has
picked up speed.the reduced voltage is obtained by using a
starter.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / jitendra singh
control starting current and torque...... but current should not be controlled at the expense of torque....
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vetriselvi
starters are used for reducing the starting currrent
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suman
small induction motors up to 3H.P.,may directly be switched on to supply mains ,but those of larger capacity must use some type of starting device or starter.the function of starter is to limit the current at the time of start, which is about 5 times the full load current this excessive current has two major upsetting effects 1. it produces large voltage drop in the distribution network and causes voltage regulation of the supply system 2.it may cause disturbance in stopping of the motor which are already running on the same supply line Four types of starting methods are employed:
1.Star-Delta
2.Auto transformer method
3.Primary resistor starting.
4.Direct On-line.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vidyasagar
the current in an induction motor has the equation
i=sE/(r^2+(sx)^2)^0.5
at starting s=1
so sE=E
SO MAXIMUM EMF IS applied in the rotor circuit.hence maximum
current.to limit this high current a starter is used
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / angel
starter is required to limit the current and starting the
torque and also increases.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / puja
to reduse the starting current ,so that no ohmic losses in
the windings
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / eugine augustine
Starters are used in Squirrel Cage Induction Motors for the
following reasons:-
1. To provide several switching on and off operations by
means of the Contactor whose special contacts can withstand
high starting currents and switching off surges.
2. To provide lower starting currents at starting for
larger HP Motors, thereby preventing severe voltage drops in
the line which may affect other running equipments.
3. To provide protection against overload and single
phasing by means of the thermal magnetic Overload relay
provided in the Starter.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sharif
at starting, The relative speed between the field and the stationery conductor (the rotor) is maximum and the resistance of winding is very small. If rated voltage is applied to the motor a current of 500%-800% of nominal current is drawn from the the supply. The starting current will be diminished when the rotor picks up speed. This high starting current will heat up the motor and may also damage insulation. The starting toque, which is proportional to the squared of the voltage will also be massive and might damage the load connected to the shaft of the motor. Another Important factor is the voltage dip in the network due to the sudden withdrawal of large current from the network. To overcome all these problems, a starter is used especially for big industrial motors. Factors, such as size of the motor, type of load, duty cycle and the environment are important when selecting a particular starter for a motor. The best starters are soft-starters and variable speed drives (V.S.D). With the use of VSDs, you can limit the starting current and also regulate the torque -speed characteristics of the motor as per requirements of the load.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / divvela adhi sekhar
at the time of starting slip is maximum that is <1> and rotor speed is zero emf depends upon synchronous speed and actual speed generally this starting is 5 to 8 times of full load current. this current damages the circuit thats why the starter is required
| Is This Answer Correct ? | 0 Yes | 0 No |
I want formula to calculate current loss with distance in km.I searched many sites but didn't right answer.Plz reply me
Can you please explain creepage distance in detail, for a 6.6kV cable head what must the distance be and how do you determine it?
What is the Diesel consumption between 82KVA DG Set and 180KVA DG Set for 1 hour.
why neutral grounding transformer is used for generator and why it is not used for transformers?
Main advantage of auto transformer over two windings transformer is that A it needs no cooling B it uses only one winding C core losses are reduced D it has simple construction
Size of the power cable like 1.5,2.5,4 sq.mm which area calculated from whick area or how specified the size?
Define resonant peak?
WHAT IS LIGHTNING,HOW TO CALCULATE LIGHTNING DESIGN CALCULATION?
What is class ab operation?
in india,we use 230V,50 Hz,whereas many other countries use 110V,60Hz.what r d advs and disadvantages of each of them?
What is the permissible limit of shaft voltage for 6.6 KV motors ? Why? Is there any standard is available?
How 48-relay (incomplete sequence) functions?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)