Answer / manish joshi

1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100 is used in RTD and
normally 6Nos can be used

2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing

3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip

4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.

5. SPM Nipples: for vibration monitoring

6. Seperate terminal box for space heater.

Is This Answer Correct ?    23 Yes 0 No

What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / pramod_wank

The answer of manish joshi is correct some correction as follows
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100(2mA) is used in RTD
and
normally 6Nos can be used(In each winding 2nos RTD)

2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing (In each side 2RTD used Drive side end
(BE) & non drive side end(NDE))the total 4RTD required

3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip.(DTT normally used for drive side end &
non Drive side end at max 250v,5A)

4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.

5. SPM Nipples: for vibration monitoring (for drive & Non
Drive Side end)

6.Seperate terminal box for space heater(1ph,240v,300w).

7.Greasing Nipple for Drive & Non drive End.

8.Vibrating Sensor at drive side.

9.Main Terminal box to coonect the supply 415V AC.

10 Neutral terminal Box if required

11.Lifting Hook to lift the motor

12.Earting Bolt as per your electrical system.

Is This Answer Correct ?    16 Yes 1 No

What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / jagannath_sila

to give the motor with a given ckt we requir as motor
contact module of given rating.
in this module we get ckt
breaker.isolator&contactor.normally the contactor rating is
32 amp.

Is This Answer Correct ?    5 Yes 4 No




What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / nagaraj .n

insulation tester,test lamp,supply wires,rated type fuse,
( T P D T SUPPLY BOARD breaker.isolator&contactor.

Is This Answer Correct ?    3 Yes 2 No

Post New Answer



More Electrical Engineering Interview Questions

can we connect PARALLEL 2 D.G set with different rating?? How ? What is the requirement for this connections?

1 Answers   Amoli Organics,


should Dy11 and Dy1 group can be operated in parallel??????

1 Answers  


IF avr is voltage regulator of genset means why we are giving genset CT sense to AVR ?

3 Answers   ABB,


Difference between 3.5 core and 4 core

2 Answers  


Why in earthing, the earthing plate is put in vertical position? and further what is soft coke that is used in earthing?

2 Answers   Wipro,






What are test values for an 63 KVA and 100 Kva Distribution Transformers for the following typical tests 1)Magnetic balance 2)Short circuit test 3)Open Circuit test 4)Vector group confirmation test .please give me the standard values for all the above tests.

0 Answers  


what is the disadvantages of common earthing for AC and DC equipment? (i am talking about inverter control room and inverter duty transformer earthing is common...?)

0 Answers   TATA,


why on delay timer used for fully automatic star delta starter?

0 Answers  


what is proper capacitor placement? How to evaluate capacitor size?

0 Answers   CPCL,


what is the capacity of storing mass electricity.

1 Answers  


The power dissipated by a resistor of 10ohm when a current of 2A passes through it is:(a) 0.4W(b) 20W(c) 40W(d) 200W

2 Answers  


how to calculate short circuit breaking capacity KA for 2500kva 33kv transformer.

0 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (4642)
  • Mechanical Engineering Interview Questions Mechanical Engineering (3703)
  • Electrical Engineering Interview Questions Electrical Engineering (15783)
  • Electronics Communications Interview Questions Electronics Communications (2638)
  • Chemical Engineering Interview Questions Chemical Engineering (762)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (79)
  • Bio Engineering Interview Questions Bio Engineering (30)
  • Metallurgy Interview Questions Metallurgy (95)
  • Industrial Engineering Interview Questions Industrial Engineering (199)
  • Instrumentation Interview Questions Instrumentation (2883)
  • Automobile Engineering Interview Questions Automobile Engineering (171)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (41)
  • Marine Engineering Interview Questions Marine Engineering (62)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Engineering AllOther Interview Questions Engineering AllOther (1335)