What accessories required to give the motor with given
circuits and do you know the ratings of those accessories?

Answers were Sorted based on User's Feedback



What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / manish joshi

1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100 is used in RTD and
normally 6Nos can be used

2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing

3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip

4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.

5. SPM Nipples: for vibration monitoring

6. Seperate terminal box for space heater.

Is This Answer Correct ?    25 Yes 0 No

What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / pramod_wank

The answer of manish joshi is correct some correction as follows
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100(2mA) is used in RTD
and
normally 6Nos can be used(In each winding 2nos RTD)

2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing (In each side 2RTD used Drive side end
(BE) & non drive side end(NDE))the total 4RTD required

3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip.(DTT normally used for drive side end &
non Drive side end at max 250v,5A)

4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.

5. SPM Nipples: for vibration monitoring (for drive & Non
Drive Side end)

6.Seperate terminal box for space heater(1ph,240v,300w).

7.Greasing Nipple for Drive & Non drive End.

8.Vibrating Sensor at drive side.

9.Main Terminal box to coonect the supply 415V AC.

10 Neutral terminal Box if required

11.Lifting Hook to lift the motor

12.Earting Bolt as per your electrical system.

Is This Answer Correct ?    17 Yes 1 No

What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / nagaraj .n

insulation tester,test lamp,supply wires,rated type fuse,
( T P D T SUPPLY BOARD breaker.isolator&contactor.

Is This Answer Correct ?    4 Yes 2 No

What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / jagannath_sila

to give the motor with a given ckt we requir as motor
contact module of given rating.
in this module we get ckt
breaker.isolator&contactor.normally the contactor rating is
32 amp.

Is This Answer Correct ?    5 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

WHICH TYPE OF TRANSFORMER IS USED IN POWER TRANSMISSION BASED ON TRANSFORMER CONNECTION ON PRIMARY AND SECONDARY SIDE

3 Answers  


Dear Sir I am living in Jaipur Rajasthan  now I did complete my b tech degree in electrical engineering in 2012  Sir how I gate certificate of competency for electrical supervisor

0 Answers   ONGC,


When geneartor is running in poor lagging side power factor its excitation current increases then it is running in improved lagging side.Kindly tell me when gen is running in leading side what will happen

3 Answers  


What will happen if power transformer designed for 50 Hz is connected to 500 Hz of the same voltage , and vice versa ?

1 Answers  


how does the rotating m.m.f is produced in the 3-phase induction motor and how the poles are created in 3-phase induction motor ?

0 Answers  






why spark is produced in mosquito bat?and what are the ways to reduce it?

2 Answers   Godrej,


How to decide whether A / B / C / D curve type MCB should be used?

0 Answers  


How to improve fuel cell in a distribution system?

0 Answers  


What happen if two protection core (3p) of VT in LAVT are 11kv/root3, 110v/root3 and one protection core (3p) is 11kv/root3, 110v/3

1 Answers  


how did the differential relay work to protect the power transformer

4 Answers  


on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf  has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure? 

2 Answers  


what is the formula to find out how many amps generater takes running on full load.

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16636)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)