What accessories required to give the motor with given
circuits and do you know the ratings of those accessories?




Answers were Sorted based on User's Feedback



What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / manish joshi

1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100 is used in RTD and
normally 6Nos can be used

2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing

3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip

4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.

5. SPM Nipples: for vibration monitoring

6. Seperate terminal box for space heater.

Is This Answer Correct ?    22 Yes 0 No

What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / pramod_wank

The answer of manish joshi is correct some correction as follows
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100(2mA) is used in RTD
and
normally 6Nos can be used(In each winding 2nos RTD)

2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing (In each side 2RTD used Drive side end
(BE) & non drive side end(NDE))the total 4RTD required

3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip.(DTT normally used for drive side end &
non Drive side end at max 250v,5A)

4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.

5. SPM Nipples: for vibration monitoring (for drive & Non
Drive Side end)

6.Seperate terminal box for space heater(1ph,240v,300w).

7.Greasing Nipple for Drive & Non drive End.

8.Vibrating Sensor at drive side.

9.Main Terminal box to coonect the supply 415V AC.

10 Neutral terminal Box if required

11.Lifting Hook to lift the motor

12.Earting Bolt as per your electrical system.

Is This Answer Correct ?    16 Yes 1 No

What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / jagannath_sila

to give the motor with a given ckt we requir as motor
contact module of given rating.
in this module we get ckt
breaker.isolator&contactor.normally the contactor rating is
32 amp.

Is This Answer Correct ?    5 Yes 4 No




What accessories required to give the motor with given circuits and do you know the ratings of tho..

Answer / nagaraj .n

insulation tester,test lamp,supply wires,rated type fuse,
( T P D T SUPPLY BOARD breaker.isolator&contactor.

Is This Answer Correct ?    3 Yes 2 No

Post New Answer



More Electrical Engineering Interview Questions

should %impedance be high or low in a power transformer? if so why?

0 Answers  


why the voltage level in transmission line are in multiple of 11kV, 22kV, 33 kV etc..( i.e., 220 V )?

4 Answers  


Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.

0 Answers   HAL,


Difference between divercity and power factor

1 Answers  


length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?

2 Answers  






Please tell me the formulaes while designing a substation for power Calculations in designing a 33 KV Substation?????

0 Answers  


Transformer calculation

1 Answers   Aramco, LMW Lakshmi Machine Works Limited,


WHY WE ARE DOING THE EARTHING IN A SYSTEM. SOME PEOPLE ARE TELLING FOR PROTECTION. WHAT PROTECTION GIVE ME THE CORRECT ANSWER.

2 Answers  


how much current will be drawn by 3 phase, 415v, 50 hz, 20 ton central ac

3 Answers  


What happened ,If 3 phase clearance not maintained in 33KV Line,11KV LIne etc?

0 Answers  


what do you call the last pole on a overhead line near a substation

2 Answers  


What is meant by Active and reactive power?

8 Answers   Micron Electricals, SVIT,






Categories
  • Civil Engineering Interview Questions Civil Engineering (4638)
  • Mechanical Engineering Interview Questions Mechanical Engineering (3701)
  • Electrical Engineering Interview Questions Electrical Engineering (15777)
  • Electronics Communications Interview Questions Electronics Communications (2637)
  • Chemical Engineering Interview Questions Chemical Engineering (762)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (79)
  • Bio Engineering Interview Questions Bio Engineering (30)
  • Metallurgy Interview Questions Metallurgy (95)
  • Industrial Engineering Interview Questions Industrial Engineering (199)
  • Instrumentation Interview Questions Instrumentation (2879)
  • Automobile Engineering Interview Questions Automobile Engineering (171)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (41)
  • Marine Engineering Interview Questions Marine Engineering (62)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Engineering AllOther Interview Questions Engineering AllOther (1334)