What accessories required to give the motor with given
circuits and do you know the ratings of those accessories?
Answers were Sorted based on User's Feedback
Answer / manish joshi
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100 is used in RTD and
normally 6Nos can be used
2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing
3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip
4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.
5. SPM Nipples: for vibration monitoring
6. Seperate terminal box for space heater.
| Is This Answer Correct ? | 25 Yes | 0 No |
Answer / pramod_wank
The answer of manish joshi is correct some correction as follows
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100(2mA) is used in RTD
and
normally 6Nos can be used(In each winding 2nos RTD)
2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing (In each side 2RTD used Drive side end
(BE) & non drive side end(NDE))the total 4RTD required
3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip.(DTT normally used for drive side end &
non Drive side end at max 250v,5A)
4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.
5. SPM Nipples: for vibration monitoring (for drive & Non
Drive Side end)
6.Seperate terminal box for space heater(1ph,240v,300w).
7.Greasing Nipple for Drive & Non drive End.
8.Vibrating Sensor at drive side.
9.Main Terminal box to coonect the supply 415V AC.
10 Neutral terminal Box if required
11.Lifting Hook to lift the motor
12.Earting Bolt as per your electrical system.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / nagaraj .n
insulation tester,test lamp,supply wires,rated type fuse,
( T P D T SUPPLY BOARD breaker.isolator&contactor.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / jagannath_sila
to give the motor with a given ckt we requir as motor
contact module of given rating.
in this module we get ckt
breaker.isolator&contactor.normally the contactor rating is
32 amp.
| Is This Answer Correct ? | 5 Yes | 4 No |
150 hp moter how many kwh in 1 hour and what forfula 3 phase kwh.
5 Answers College School Exams Tests, CPCL, Syncom, Thermax,
Pls explan the OLR setting in VCB at HT yard
Is 3C x 2.5 Sqmm Cable can withstand 40Amp Starting current? If Yes then specify your ans.
How to increase the specific gravity of DG batteries?
A 400KVA transformer has 400 Hz frequency. If the frequency is changed to 50 Hz, then what will be the new KVA rating?
What is the meaning of transformer 16 / 20 mva.
While testing a ZCT what parameters have to check or measure?
why secondary terminal of current transformer should not be open circuited?
Briefly describe means used by electricity suppliers to influence the flow of active and reactive power in power networks (one for each type)?
what is let through energy of mccb
can i use the six sigma method which is used in management area, in state estimation of power systems?
How to select transmission line type (i.e. 11kv or 33kv) for new established industries
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)