Between Star-Delta & Star-Star Power transformer which one
is efficent for Earth Fault?
Answers were Sorted based on User's Feedback
Answer / daher
star/star because in the case of line to earth faults the
zero curret IO in delta connection transformer has no path
to leave the close loop of three phases transformer
Is This Answer Correct ? | 17 Yes | 8 No |
Answer / nidhi
star delta .
because in star star connection solidal grounding should be
provided to ground third harmonics. in star delta whenever
afault will occur then it will circulate only in this delta
not go to the output
Is This Answer Correct ? | 12 Yes | 5 No |
Answer / sunil guru
Star - Star bcz.. it has a point at center which can be
used as a neutral or can be grounded,
but in case of star-delta there is no path for ground
return current during short circuit..an the circulating
current will flow inward itself and can damage the winding..
for any disagreement mail me at parmar20072008@yahoo.com
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / awais
Star star because for earth fault return path is required to complete the circuit so neutral grounded star connection is ideal for such type of fault detection..
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / daher
star/star in case of line to ground short circuit in star -
delta transformer their is no path to I0 short circuit
current and it will turn inside the closed circuit of delta
connection
Is This Answer Correct ? | 1 Yes | 4 No |
how to calculate the change over time for star delta starter for different KW motor?
at which voltage level arcing ground is occurs ??????????
What is the gain of 1-s/1=s at 1 rad/sec?
hai now i am working as a electrical design engineer in construction field can i get a job in oil and gass field or power plant project as a electrical design engineer?
Does VT metering core can be used for synchronizing.
1 Answers Shrishti Power Technologies,
concept of busbar and load dispatching..?
What is the effect of impedance on the heat losses in case of AC system??? Does heat losses really depends on the impedance or depends only on resistive component only..??
how to calculate the cable size depending on the transformer rating
what is the unit of electricity????????????
why the efficiency of generator is more than the motor in case of swinburne's test????
why we use post insulators in no ofstacks at substation for supporting equipment ? why we not use single post insulator
In auto transformer if power transferred inductively and conductively are same, the ratio of output/input voltage is A 1 B 0.7 C 0.5 D none of above