what type of relays used in transformers?
Answers were Sorted based on User's Feedback
There are many types of protection relays used in
transformers depend upon its construction, size, use etc.
They are
1. Buchholz relay for incipient faults like short ciruit,
winding temparature protection, oil temparature protection,
oil level protection, oil pressure protection, Pressure
relief valve (for oil filled transformers)
2. Differential protection
3. Thermal Protection
4. Earth fault protection
5. Over current protection
6. Over excitation protection(where OLTC is used) etc
| Is This Answer Correct ? | 64 Yes | 5 No |
Answer / murthy
for internal faults(incipiant faults) buch holz relaysare
used, over current relays also used in transformers
| Is This Answer Correct ? | 39 Yes | 3 No |
Answer / minal
Bucholz relay is used in oil filled transformer.These
relays sense the gas & trip the transformer before a fault
is occured.
Indoor type of transformers(without conservators) are
equipped with sudden pressure relays, which performs a
similar function like bucholz relay.
| Is This Answer Correct ? | 32 Yes | 3 No |
Answer / vishal
BUCKHOLTZ RELAYS(OIL COOLED T/F)---->INCIPIENT INTERNAL
FAULTS
PERCENTAGE DIFF PROTECTION----->FOR SHORT CIRCUITS(FOR
>1MVA T/F)
OVER CURRENT RELAY------------->SHORT CKT(FOR LOW RATING)
HAMONIC RESTRINT DIFF RELAY----->FOR PROT AGAINST MAL OPN
OF T/F
| Is This Answer Correct ? | 24 Yes | 3 No |
Answer / s
In protection side transformer differential,ref,stand by
earth fault,o/c & e/f, transfomer trouble function relay
| Is This Answer Correct ? | 28 Yes | 13 No |
Answer / sethu siva & mainkandarama
1)Differential protection (If transformer is more than 5
MVA :As per IS 2026)
2)Restricted earth fault protection
3)Stand by earth fault protection
4)O/C & E /F protection (if required)
5)Over flux (V/F)
Auxiliary protections
1)B' relay protection
2)PRV
3)Oil temp. high trip
4)Winding temperature high trip
5)OSR
Alarms:
1)Winding temp. high alarm
2)Oil temp. high alarm
3)MOG alarm
| Is This Answer Correct ? | 15 Yes | 1 No |
mainly bucholz relay which having important role for
protection system.after auxilary relay for oil andwinding
temprature alaram and tripping protection
over current relay for phase to phase protection after E/F
relay and master trip relay provided in oil filled
transformer protectin.
| Is This Answer Correct ? | 7 Yes | 0 No |
What is the advantage of AC supply?
What are the types of piano switches?
Why NGR is provided in sub station?
how does calculate loss correction factor in transformer
We have 90mX100m hangar with 16 no.of supporting pillar. It is required to provide power supply on all pillars. what is suggested earthing scheme for hangars.
coil is consist of
What is PIR (pre inserting resistance) in 400kv EHV SF6 BREAKER? Why it use?
The 3 phase 400 hp 440 volt slip ring induction motor do not take one phase amps why ? The motor is running good condition
Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..
why table fans rotate clockwise .while ceiling in anti clockwise?
When we give supply to a transformer 11 kv and we get 415v from it, so when we give supply to same transformer 415v on ht side what we get? and When we gives supply to any transformer to L.T. side 415v or 220v What supply is on H.T. side?
how do we calculate cable sq mm size,that if 50 A load
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)