If a HV Underground Cable (13.8KV) is layed in the ground below 1.5 Mtrs and any building construction is done on the Cable route. IS this allowable or Not? What should be the clearance. As per ISO construction on HV cable route is safe or Not? Why? Can any body suggest the site for my question?
Answer / ra
cables for 13.8 kv is consider to be medium voltage (not HV ) and if it is routed in cable duct so there is no issue.the purpose of cable duct is to provided safety to cable route.
in case if the cable buried in ground, executor of building construction should notify the client through technical query to solve the issue by technical way according to specification and standard.
in my opinion builder suppose to keep opening for cable routing
Is This Answer Correct ? | 0 Yes | 0 No |
In the formula : Knee point voltage = Burden X alf / class, Please inform what is alf? regards Shashidhar M.R.
what happens if the phase sequence of parrlel connected sys will changed & phase displacement
WHAT IS MEAN BY MAGNETIC LOCKING
IN A MAGNETIC MATERIAL HYSTERYSIS LOSS CAN'T BE REDUCED TO ZERO. HY?
What is trip and closing coil in cb? Why need of them
Can you any one explain application of buccholz relay operation and pressure relif device operation of power transformer
What is the difference between Busbar Chambar, MCCB board and MCB Board? How to choose to use which one in the system?
how we can check that any motor is faulty may be single phase or three phase?
transformer phasor diagram under load explain it?
fuel-air ratio in a petrol engine fitted with suction carburettor,operating with dirty air filter as compared to clean filter will be
WHAT IS THE DIFFERENCE BETWEEN SHOP DRAWINGS/ DESIGN DRAWINGS AND AS BUILT DRAWINGS??
2 Answers ACC, Al-Jaber, Dubai Group, ECEC,
how many transformer