what type of relays used in transformers?
Answers were Sorted based on User's Feedback
Answer / maha
The anser is Differential relay because the examinor asked
the question in the sense of power tranformer. but buch
hole relay is used for tranformer internal faults..
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / j.ramkumar
over voltage reley
over current reley
earth fault reley
dv/dt relay
diff relay
bocolz relay
surge protection relay
over fluxing relay
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / g.v.suresh kumar
BUCHLOZ RELAY IS USED FOR INCIPITENT FAULTS
PERCENTAGE DIFFERENTIAL RELAY IS USED FOR INTERNAL FAULTS
AND EXTERNAL FAULTS
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / v.c.k
Buchholz relay
Gas Pressure/Oil and winding temperature relay provided
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / gopi
yes, we can use buchhloz relay to protect the transformers.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / anjani kumar
For internal fault buchholz relay
is used while external fault differential relay is used.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / paul
1.Differential Relay or
2.Overall differential Relay
3.Overflux Relay
4.Buchholz Relay (Only for oil immersed transformers, but widely used)
5.OLTC Buchholz Relay
6.PRV Relay
7.OT
8.Trip Relay
9.WT Trip Relay etc....
| Is This Answer Correct ? | 3 Yes | 0 No |
how to find transformation ratio of squirrel cage induction motor
why are the transmission lines operated at 220 kv nly... nt les dan dat...
What is the limitation of kirchoffs law?
how calculate busbar size for rated amps, which formula use
DESCRIBE THE CONSTRUCTION ANDOPERATION OF BELT CONVEYORS AND SCR CONVEYORS , DRAW NEAT SKETCHES
How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.
WHY EARTHING NOT NEEDED IN BATTERY IN SUBSTATION?
in Megger what type of voltage(AC or DC) are produce.how they work.
If 11 KV breaker on the primary side of a 11 KV/3.3 KV 12.5 MVA transformer can be installed at a distance of 1000 mtrs through a 11 KV cable. If no what are the probable reasons.
why the frequency in india is 50 50HZ why we not select the o ther frequncy range?
When we synchronize the Generator BKR with TIE BKR then Gen BKR is hold but TIE BKR is Tripped on Non directional over current but when TIE BKR is Syn. with Gen. BKR then no fault occur so what is the problem
i need 24v dc from 230v ac supply how we can getit ? what are the devices &its rating requied for that ? plzz i need answer urgently .thank u
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)