can we use a control valve without positioner
Answers were Sorted based on User's Feedback
Answer / ashish namdev
YES
1. put air pressure at a certain value (according max air requirement for actuator full action )
2. then connect limit switch at several position (0-100 scale)
3. then make a logic for open & close control action with use limit switch feedback.
4. connect air inlet with solenoid or pilot valve.
Ashish Namdev (Sr. Engg)
Jaypee Power Plant,
Bina (MP)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kamesh.g
No we can not control the control valve without positioner
eccept on-off type control valves ,Positioner main purpose
is boostup the air signal from I/P and put the position as
per your requirement ( Command)positioner link rod will
give the feedback to control valve air command air supply
so it can adjust the valve in correct position.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / m.ra
Yes we can operate a control without a positioner in the
following condiotions.
1) Volume booster is not required.
2) Operation of control valve will be very sluggish.
3) Charecteristics of control valve cannot be changed.
4) If the valve is self regulation than also positioner is
not required.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / ajith294
here more answers reagrading positioner
maximum of the answers are 'YES' especially Answer number
10,
then i have a doubt that how control a valve at 50% open,
with out a positioner.
if there is not a positioner, how we can control the valve
( control the pnumatic pressure is applied the
actuator)?????
if a valve it using fully open of fully close condtion
throgh Solenoid Valve ( bypass the air to actuator) is on
off valve.
Without a positioner we cannot control the valve through a
controller.
thanks
| Is This Answer Correct ? | 1 Yes | 6 No |
Answer / sandy
The name itself indicates the function of the positioner. A
control valve without positioner will act as a ON-OFF valve.
| Is This Answer Correct ? | 13 Yes | 21 No |
Answer / yogesh
On-off control valve can use without positioner. but globe
control valve can not use without positioner.
| Is This Answer Correct ? | 6 Yes | 24 No |
why we use 0.2 to 1.0 kg/cm2 output in control valve
what is flow equation of kg/hr to m3/hr
What is zone,loop/fire alarm system?
micromotion flow meter used for
how the flow rate is measured from a pipe with the help of pressure?
centrifugal compressor interlock? Tell me the parameter at which compressor will trip
how to calibrate differential pressure switch
What is the working principle of the magnetic meter?
When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?
what do you mean by CJC (cold junction compensation).?
How to O2 analyzer works?
wht is mean by dpt(differential pressure transmitter)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)