can we use a control valve without positioner
Answers were Sorted based on User's Feedback
Answer / ashish namdev
YES
1. put air pressure at a certain value (according max air requirement for actuator full action )
2. then connect limit switch at several position (0-100 scale)
3. then make a logic for open & close control action with use limit switch feedback.
4. connect air inlet with solenoid or pilot valve.
Ashish Namdev (Sr. Engg)
Jaypee Power Plant,
Bina (MP)
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kamesh.g
No we can not control the control valve without positioner
eccept on-off type control valves ,Positioner main purpose
is boostup the air signal from I/P and put the position as
per your requirement ( Command)positioner link rod will
give the feedback to control valve air command air supply
so it can adjust the valve in correct position.
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / m.ra
Yes we can operate a control without a positioner in the
following condiotions.
1) Volume booster is not required.
2) Operation of control valve will be very sluggish.
3) Charecteristics of control valve cannot be changed.
4) If the valve is self regulation than also positioner is
not required.
Is This Answer Correct ? | 4 Yes | 8 No |
Answer / ajith294
here more answers reagrading positioner
maximum of the answers are 'YES' especially Answer number
10,
then i have a doubt that how control a valve at 50% open,
with out a positioner.
if there is not a positioner, how we can control the valve
( control the pnumatic pressure is applied the
actuator)?????
if a valve it using fully open of fully close condtion
throgh Solenoid Valve ( bypass the air to actuator) is on
off valve.
Without a positioner we cannot control the valve through a
controller.
thanks
Is This Answer Correct ? | 1 Yes | 6 No |
Answer / sandy
The name itself indicates the function of the positioner. A
control valve without positioner will act as a ON-OFF valve.
Is This Answer Correct ? | 13 Yes | 21 No |
Answer / yogesh
On-off control valve can use without positioner. but globe
control valve can not use without positioner.
Is This Answer Correct ? | 6 Yes | 24 No |
WHY WE R NOT USING THE TURBINE FLOW METER IN THE STREAM SERVICE ? pl explain?
what are procedure of sox-nox calibration
Draw bode plot of any transfer function. Why is plotting bode necessary?
what is absolute pressure and where use in process?
What does a fire detector detects?
Identify and use the ANSI/ISA-S5.1 consensus industrial standard process symbols.
What is the difference between compensation and extension cable.
What are the types of valves?
Describe the typical instrumentation used in monitoring the performance of a shell and tube heat exchanger.
what is difference between Floating D.C.Voltage and Fixed D.C.Voltage?
i have a dp tx range is 5000mmwc. in which calibration i use in a open tank.1.5*3.5*2.5 mtr.for level msmnt. what is the calculation.
what are the inputs (drawings) we need to prepare loop schematics??