Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to Calibrate variable Head flowmeter (Orifice), here we
dont know High pressure and low pressure then how to apply
pressure on HP and LP side ?



How to Calibrate variable Head flowmeter (Orifice), here we dont know High pressure and low pressu..

Answer / carl_ellis

The situation must be an installed, running system, with a receiver that displays a flow rate from the DP pressure signal, because no one just has a DP transmitter across an orifice plate for fun.

Every differential pressure primary flow element is assumed to be zero flow at zero DP. So the DP low side pressure 'zero' will always be zero DP, or when the 3 valve manifold has its process connection valves closed and the equalizing valve open.

The measured DP represents some flow rate on the square rooted curve of the normalized percentage of span.

In order to determine the DP span value, you measure the actual DP and note what the flow rate reads on the receiver (PLC/DCS/recorder/indicator/controller) at that DP.
Then you can calculate what the DP span value is for the max flow rate that receiver is configured for.

The receiver has some configured flow range: 0-500gpm? 0-1,000 bpd? 0-650pm? Find out what it is.

For example, say you measure a DP value of 700mm wc and that 700 mm wc shows a flow rate reading of 264.5 lpm on the receiver.

You have discovered that the receiver is scaled 0-500 lpm for that DP transmitter and the receiver does the square root extraction.

What is the flow rate as percentage of flow span?
264.5 lpm/500 lpm = 52.9% of flow rate span

52.9% normalized is 0.529

Since the flow rate is the square root of the normalized DP span, you need to square the normalized percentage of flow rate to find the equivalent percentage of DP span.

0.529^2 = 0.2798, or 27.98% (~ 28%) of the DP span.
If 700mm is 28% of span, 100% of span is 2500mm wc.

So the DP span for the transmitter is 0 (no flow) to 2500mm wc (max flow).

Carl Ellis
Measure First

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

How LVDT position transmitter works on DC supply(24vdc) from DCS, whereas transformer operates on AC supply? pls help..

1 Answers  


In a class of 150 students, 40 passed in Social Studies, 90 passed in Science and 30 failed in both the subjects. vi)How many students passed in at most one subject among Science and Social Science?

7 Answers   CAT, CGI, Cipla, KHK, Visa,


So I'm a first year apprentice and I'm having a tough time with knowing the difference between AI, AO, DI, DO. I'm having a hard time understanding what devices are which and why. Can someone explain this to me?

2 Answers  


What is the procedure of DP switch calibration 

2 Answers   NOCL,


1. How can leveltrol be installed in steam drum for measuring the level of steam drum?

1 Answers   Fischer,


Why we use 3-15 psi air for control valve input?

2 Answers  


what is the advantage of submersible level transmitter compare to ultrasonic level transmitter?

0 Answers  


please send the hpcl (instrumentation) model placement papers to my mail....

9 Answers   HPCL, Invensys, IOCL, ONGC,


What is Process portal A(PPA)?

1 Answers   ABB,


A pressure transmitter with a range of 0-100 bar.The accuracy of the instrument is 1% of upper range value? The pressure indicating transmitter is showing the system pressure is 50 bar. b. When you include the error, what is the minimum possible pressure in our fuel gas system? i. 49.5 bar ii. 49 bar iii. 1 bar iv. 0.5 bar We want to change the filter cartridge. We must depressure the fuel gas system. c. After we depressure the system in preparation for maintenance, the transmitter displays a pressure of +0.1 bar. At this time, what is the possible range of pressures in our fuel system? i. +0.099 to +0.101 bar ii. 0 to +0.2 bar iii. -0.1 to +0.3 bar iv. -0.9 to +1.1 bar

3 Answers  


Define magnetic flow meter and mass flow meter.

1 Answers   Ramco,


Which type of diaphragm use in costic line, dm water line, natural gas line, oil line?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)