what is the minimum dielectric stregth of transformer oil.
Answers were Sorted based on User's Feedback
Answer / zahid noor
Minimum dielectric strength of transformer oil is a wrong
question itself, For New insulating transformer oil, the
value is 70kv, where as oil in use has values ranging from
25 kv to 50kv , depending upon various factors like ,
running hours of use, impurities, moisture content, sludge
content etc, but it is advisable to discard old oil, if
value does not improve after filteration above 30 KV
| Is This Answer Correct ? | 74 Yes | 14 No |
Answer / pundlik wanwe
transformer oil BD value is a relative term and as a matter
of fact we can use the oil of different break down value
depending on the transformer voltage ratings.
1) For the transformer voltage rating more or equal to 145
kv BD value of oil should be more than 65 kv and moisture
content should be below 15 ppm.
2)for the voltage rating below 145 KV BD value should be
45KV and moisture content of less than 25 ppm.
More more information please refer
a) IS: 1866 for oil in service.
b) IS: 335 for new oil
| Is This Answer Correct ? | 28 Yes | 4 No |
Answer / irfan ahmed farooqui
For a new insulating transformer oil(called virgin oil),
the,
value is 70kv for a good satisfactory level but, where as
oil in use (called in service) has values ranging from 25
kv to 50kv , depending upon various factors like ,running
hours of use, impurities, moisture content, sludge content
etc, but it is advisable to discard old oil, if value does
not improve after dehydration and filteration above 60 KV
in laboratory setup or the oil has not passing a
compatibility/mixibilty test with new transformer oil at
different ratio to come to at par in usable ranges as per
standards, on the other hand the exact values and correct
figures for Virgin oil are available in IEC-60296 AND for
oil in service there is a complete guide and specification
available as IEC-60247 where all the nesseccary
informations are available,including the test methods and
apparatus required.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / k.prakashchandra
As per IS 1866:2000,50KV for 170 KV &above,40 for
72.5-170,30 for below 72.5.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / chakri
according to BDVT 2.5MM distance withstand at min 40kv
so min dielectric strenght is 40kv
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / ajay kumar das
It should not be less then 36 KV for 1 mint.with 2.5 mm air gap
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / prasad shah
BDV of transformer oil ig generally 40 to 45 KV for used
oil.and new it is around 60 KV.Also it is depends on
incoming voltage to transformer and rating of transforemr
| Is This Answer Correct ? | 2 Yes | 1 No |
why we use the 100% and 95% stator earth fault protection for the synchronus generator ?
0 Answers Operational Energy Group,
how to compute kAIC? with formulas...
WHY PROTECTION CT IS USED NEXT TO METERING CT?
i work as a technician at a private company.. i used to take amp reading for certain appliances such as air con.. the problem is when i clamp the neutral, wire there is a current reading.. from my understanding for single phase system neutral should not have current unless if the circuit is not complete.. yet the air con still work
i want design of D.C.MOTOR 1HP 960RPM AND 2HP 960RPM ITS URRGENT
what is is the potential diffrence between two phase ?
Please nybody say, weather the result of Bharat Oman is declared or not? Probable date of declare???????
What will happen if the d.c. Machine is operated below rated speed?
1.what is use of isolation transformer. 2.Differance between KWH,KVAH,KVARH,KVA. 3.Main use of the CT and PT.
How can ou verify the size of conductor 50Sq.mm ACSR
0 Answers Adani Power, Apar, EFS, Polycab, WHF,
why is one voltage transformers (instead of three ) installed at the entrence of the incoming line in a substation.
What are the classification of Servo Motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)