what is the minimum dielectric stregth of transformer oil.
Answers were Sorted based on User's Feedback
Answer / zahid noor
Minimum dielectric strength of transformer oil is a wrong
question itself, For New insulating transformer oil, the
value is 70kv, where as oil in use has values ranging from
25 kv to 50kv , depending upon various factors like ,
running hours of use, impurities, moisture content, sludge
content etc, but it is advisable to discard old oil, if
value does not improve after filteration above 30 KV
Is This Answer Correct ? | 74 Yes | 14 No |
Answer / pundlik wanwe
transformer oil BD value is a relative term and as a matter
of fact we can use the oil of different break down value
depending on the transformer voltage ratings.
1) For the transformer voltage rating more or equal to 145
kv BD value of oil should be more than 65 kv and moisture
content should be below 15 ppm.
2)for the voltage rating below 145 KV BD value should be
45KV and moisture content of less than 25 ppm.
More more information please refer
a) IS: 1866 for oil in service.
b) IS: 335 for new oil
Is This Answer Correct ? | 28 Yes | 4 No |
Answer / irfan ahmed farooqui
For a new insulating transformer oil(called virgin oil),
the,
value is 70kv for a good satisfactory level but, where as
oil in use (called in service) has values ranging from 25
kv to 50kv , depending upon various factors like ,running
hours of use, impurities, moisture content, sludge content
etc, but it is advisable to discard old oil, if value does
not improve after dehydration and filteration above 60 KV
in laboratory setup or the oil has not passing a
compatibility/mixibilty test with new transformer oil at
different ratio to come to at par in usable ranges as per
standards, on the other hand the exact values and correct
figures for Virgin oil are available in IEC-60296 AND for
oil in service there is a complete guide and specification
available as IEC-60247 where all the nesseccary
informations are available,including the test methods and
apparatus required.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / k.prakashchandra
As per IS 1866:2000,50KV for 170 KV &above,40 for
72.5-170,30 for below 72.5.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / chakri
according to BDVT 2.5MM distance withstand at min 40kv
so min dielectric strenght is 40kv
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / ajay kumar das
It should not be less then 36 KV for 1 mint.with 2.5 mm air gap
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / prasad shah
BDV of transformer oil ig generally 40 to 45 KV for used
oil.and new it is around 60 KV.Also it is depends on
incoming voltage to transformer and rating of transforemr
Is This Answer Correct ? | 2 Yes | 1 No |
testing of Vector Group – YNaoD II
We are dealer in Maharashtra State & We have recd. form C from dealer of Maharashtra State against our E-1 form. Now assessing authority is asking for counterfoil of our E-1 form. But, our E-1 form counterfoil is misplaced somewhere & assessing authority is disallowing the C form which is recd. from Maharashtra State.Please let us know the option for allowing C form?
How check electrical motor winding.
WHY STABILIZER SHOULD USED
How to test IR testing & magnetic balance test
could i arrange a faulty and healthey battery bank togather in parallel , if your ans is not then why?
For 132 KV line, PT or CVT which is prefered for measuring & protection? is there any IS or IEE standard available?
the voltage per turn of a primary winding of a transformer is the same as the voltage per turn of the secondary winding of the transformer. why?
What is the full form of GSL wire
Mention how NPN and PNP transistor works?
what is the reason for choosing DYn11 in transformer, why not DYn12 or something else
will we have to design the UPS differently for both i.e. if we want to connect the two batteries in parallel and/or we want to connect the two batteries in series ?