what is the minimum dielectric stregth of transformer oil.
Answer Posted / pundlik wanwe
transformer oil BD value is a relative term and as a matter
of fact we can use the oil of different break down value
depending on the transformer voltage ratings.
1) For the transformer voltage rating more or equal to 145
kv BD value of oil should be more than 65 kv and moisture
content should be below 15 ppm.
2)for the voltage rating below 145 KV BD value should be
45KV and moisture content of less than 25 ppm.
More more information please refer
a) IS: 1866 for oil in service.
b) IS: 335 for new oil
| Is This Answer Correct ? | 28 Yes | 4 No |
Post New Answer View All Answers
hey guys i scored 910 on GRE and 67 on TOEFL respectively.I have an aggregate of about 74%in my B tech.For which colleges should i apply for an MS program in electrical engineering.I am looking for colleges in NJ,SC,NC,GEORGIA, NY. Please reply with a good response.....
What is NGR . What is the purpose of 10 sec ,60 sec rating of NGR.
Why synchorised generators are used for the production of electricity?
How the PF control while running DG set with load
what is the difference between fault current ant short circuit current?
What is the direction of current flow in ct secondary...means if the current is flowing from P1 to P2 then what will be the direction of current flow in ct secondaryw
Define bibo stability.
What is VSCF windelectrical system?
Why field rheostat is kept in minimum position?
what is the standard values(Megger test) of resistances between L&N,L&E and N&E for a system on IEE regulations?
What is the limitation of kirchoffs law?
magnetizer priciple
what is ground fault in ACB?
How to calculate no of Lighning arrestors are required for protecting 50mX 50m*20m cubical building and locations of LA?
132/66kv sub-station procation ?