what is the minimum dielectric stregth of transformer oil.
Answer Posted / pundlik wanwe
transformer oil BD value is a relative term and as a matter
of fact we can use the oil of different break down value
depending on the transformer voltage ratings.
1) For the transformer voltage rating more or equal to 145
kv BD value of oil should be more than 65 kv and moisture
content should be below 15 ppm.
2)for the voltage rating below 145 KV BD value should be
45KV and moisture content of less than 25 ppm.
More more information please refer
a) IS: 1866 for oil in service.
b) IS: 335 for new oil
| Is This Answer Correct ? | 28 Yes | 4 No |
Post New Answer View All Answers
I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?
what are the parameters plays a major role in Potential transformer Burden calculation??
why star point of HT motor not earthed?
what kn of disc is used in 33kv,132kv,220kv,400kv,800kv transmission line
what is the minimum pay scale for electrical engineer (building construction)in kuwait? plz revert back with yrs of experience & pay scale respectively.
How many types of losses occur in a transformer?
What is the effect of positive feedback on the stability of the systems?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
I am going to appear for the RRB Chennai Section Engineer online exam. Please send me the question papers from 2001 to date to my mail id:upendrakrishna20@gmail.com,plz send me ,or send any other rrb papers plzzzzzzzzzzzzzzzzzz
What do you mean by phasors?
How to discuss the phase shift of transformer considering open delta?
why ht motors are star connected?
1.what is difference between ATS & STS main use. 2.what is difference between ACB& VCB With symobles,and main partes, manimum range. 3.How many types of relays and main function.
Which Class insulation is prefered for the sandwich Busducts ? Why?
dear all i am kumara now current working in electrical designing of control and relay panel i want learn some substaion design then any book are available. pls mention name and authour