Answer / ankamsreekar
The effective capacitance is 3 time more in delta as
compared with star connection provided that same capacitors
are used.
Is This Answer Correct ? | 19 Yes | 5 No |
Answer / sreenu
Becasue, in delta connection,voltage of three phases is
equal and the power factor( Reactive power)is depends on
voltage.
If you use star connected capacitors, the voltage may vary
due to unbalenced loading of capacitor whcih is indirectly
depends on load.
Is This Answer Correct ? | 13 Yes | 5 No |
Answer / dr. shahid
In delta the effect is 3 times as compared to when they are star connected.
Regards
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / jonathan r. lambert
Capacitors are paralleled with inductive (magnetic) loads
in delta, wye (aka "Star") and single phase AC power
sources to correct power factors so that motors,
transformers and other inductive loads appear to be
resistive. Power factor correction is a process that
cancels reactive current vectors leaving only a resistive
current. Inductive loads pull currents that contain both
resistive and reactive vectors. In power factor correction,
a capacitor's reactive current is used to cancel the
inductive reactive current created by magnetic coils in
inductive devices. If the capacitor is sized correctly the
current drawn by the capacitor will precisely cancel the
inductive magnetization current pulled by an inductive
load. The resulting motor current "seen" by the AC voltage
source will then be only resistive. Since power companies
charge for both reactive and resistive current, and since
only the resistive current is required to provide
horsepower and perform work, power factor correction
reduces the current drawn by inductive loads which reduces
the electrical operating expense. Hard to believe that
applying an additional parallel load, a capacitor, will
result in less total current but it works due to the
capacitive reactive current leading at +90 degrees and the
inductive reactive current lagging at -90 degrees, the two
parallel currents sum at the voltage source to equal zero
degrees and if the cap is sized correctly, zero amplitude.
Is This Answer Correct ? | 3 Yes | 13 No |
What is the one main difference between ups & inverter ? And electrical engineering & electronics engineering ?
Does increase or decrease of reactive load affects the Voltage.
I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.
what are different types of alternator and discuss about the methods of cooling
16 Answers Bhel, Jindal, L&T, Nalco, Vedanta,
why master trip(86) used in eletromagnet?
What does impedance in the windings of transformer signify.
Are same transformer be employed for step up and step down services?
What is the purpose of reactor in over head transmission line.Can you any explain it.
2 Answers Dr Reddys, L&T, Reddy Labs,
how to calculate the no. of turns in secondary side of CT?
why we setting 95 deg and 105 deg in wti and oti of distibution transformer ? give the reson for that ?
Why indicated only R.Y.B to phase.
how step down and step up voltage is occured in transformer