how to check the 3ph capacitor is good or not.

Answers were Sorted based on User's Feedback



how to check the 3ph capacitor is good or not...

Answer / andrew

Disconnect the capacitor from the supply and test the
capacitor terminals with a volt meter, you should have the
same voltage at these terminals as the supply voltage the
capacitor was connected to (you should probably not leave
it too long before you test the capacitor as some
capacitors tend to discharge b y themselves over time).
or you can discharge the capacitor by shorting the
terminals WITH A RESISTIVE LOAD you should never short out
a capacitor with that sort of voltage, it will be
danegerous, by using a resistive load, it will take longer
but it will be safer at least.
once you have discharged the capacitor, most decent
multimeters will have a capacitive test function, just test
the capacitor at the terminals and compare the value with
the value written on the side of the capacitpr and this
will also give you an indication of the its condition..
otherwise, call an electrician...

Is This Answer Correct ?    30 Yes 5 No

how to check the 3ph capacitor is good or not...

Answer / stanley electrician

CONNECT THE CAPACITOR TO THE SUPPLY.
CHECK THE AMPS
NOTE THE RATED AMPS IN NAME PLATE OF CAPACITOR.
IF BOTH ARE EQUAL (+ OR - 2AMPS), THEN THE CAPACITOR IS OK

Is This Answer Correct ?    31 Yes 6 No

how to check the 3ph capacitor is good or not...

Answer / suresh kumar

Switch off the all capacitor bank except one whcih u want
to check, if pf value decreasing the same time then its not
good,other capacitor can be check as same procedure.
Don't short cerkit.....
It will be dangerious.........

Is This Answer Correct ?    21 Yes 8 No

how to check the 3ph capacitor is good or not...

Answer / mohamed

check the Cpacitor Rating ( KVR) and put in the Clamp
meter take Amps

For Example = 25 KVR Capacitor
= 34 Amps ( good Condition)

Is This Answer Correct ?    19 Yes 6 No

how to check the 3ph capacitor is good or not...

Answer / sa

if the capacitor connected in capacitor bank switch off all
the capacitors except the capacitor want to test if thepf
decreasing at the moment capacitor is not good .

never short the terminals .........

Is This Answer Correct ?    14 Yes 7 No

how to check the 3ph capacitor is good or not...

Answer / hmt

chrge it for sometime.
and then remove supply and short the terminals, if you see
a spark or here some noise then they are working fine!else
they are not good for use.

Is This Answer Correct ?    42 Yes 36 No

how to check the 3ph capacitor is good or not...

Answer / uk

Disconnect the capacitor from the supply and test the
capacitor terminals with a volt meter, you should have the
same voltage at these terminals as the supply voltage the
capacitor was connected to (you should probably not leave
it too long before you test the capacitor as some
capacitors tend to discharge b y themselves over time).
or you can discharge the capacitor by shorting the
terminals WITH A RESISTIVE LOAD you should never short out
a capacitor with that sort of voltage, it will be
danegerous, by using a resistive load, it will take longer
but it will be safer at least.
once you have discharged the capacitor, most decent
multimeters will have a capacitive test function, just test
the capacitor at the terminals and compare the value with
the value written on the side of the capacitpr and this
will also give you an indication of the its condition..
otherwise, call an electrician...

Is This Answer Correct ?    7 Yes 1 No

how to check the 3ph capacitor is good or not...

Answer / selvan

3phase capacitor connected in the line,power factor
indicate the capacitor good or not.Otherwise check with
volt meter.

Is This Answer Correct ?    15 Yes 16 No

how to check the 3ph capacitor is good or not...

Answer / robert harper (ee tech)

My non fail proof but handy way is to remove the cap. from
the circuit and connect your VOM to the terminals and watch
the voltage dissipate. The set the VOM to Ohms and
reconnect the meter to the cap. and you should see the
resistance steadily go up close to infinity. You are
actually charging the cap. with the battery in the VOM.
Then recheck the voltage and you should have a low charge
and then it will dissipate again. Good cap. via non fail
proof test.

Is This Answer Correct ?    5 Yes 6 No

how to check the 3ph capacitor is good or not...

Answer / lokesh kumar

First charge the capacitor. After charging use multimeter.
If the multimeter shows any deflection, then the capacitor
is in good condition.
We can also check by connecting the two terminals, but this
is not the proper and safety way.

Is This Answer Correct ?    5 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

Can I parallel 1 MVA generator with 1kVA Generator? if V, F, Ph Seq and Ph angles are same

2 Answers  


A MACHINE WHICH HAVE 1000rpm SPEED IS LARGER IN SIZE AS COMPARED TO THAT OF A MACHINE WHICH HAVE 1500rpm.WHY ?

2 Answers  


The neutral&earth voltage is 0v.But we were connected the lighting load at the time ballast was failed.why?

1 Answers  


In 2500kva transformer how much is the withstand High voltage power frequency between primary to secondary and earth? And secondary to primary and earth?

1 Answers   Honeywell,


After synchronizing the running generator with grid, the avr getting tripped and the generator breaker also oettong tripped, before tripping the avr the pf meter of generator is showing leading pf please kindly give a suggestion to rectify this problem.

2 Answers   Thermax,


Types of test in Switchgears, MCC, NGR and DB's how it should be procced. Can anyone give me the details here or email me to pasuvaraj.k@gmail.com

1 Answers  


A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?

1 Answers  


why we use tapechanger in primary side of transformer

5 Answers   Bhel, L&T,


what is the long transmission lines

2 Answers  


In dc motor starter there is less voltage required for holding contactor that's may why it is called no volt coil. but in ac starter why holding contactor is called no volt coil.

2 Answers   JSW,


WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SIZES??

14 Answers   Dubai Group, Saudi Delta Groups, Savitha Electricals,


whats happen if we disconnect the NGR of alternator in running condition?. Generally we observed that transformer netrul is directly grounded but alternator connected with NGR, then ground?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)