what is meant by boost charge in batteries
Answer / raul
the batteries in a station are floated onto the dc bus bars
with the help of float charger i.e. all the dc requirements
r being made with the help of float charger and not by the
battery itself which is done by keeping the float charger
voltage a few volts higher than d battery voltage........in
addition to provide d.c. requirements in a
station .......the float charger provides additional few
hundreds of amperes to the battery to compensate for the
losses in d capacity of the battery due to local action
among the plates of the battery........that is why it is
also called as TRICKLE charger......in case of a.c. failure
in station, battery comes in to play and the battery starts
getting discharged........so in order to keep the battery
charged at its rated values, boost charger comes into play
and charges the battery...........and after the restoration
of the a.c. supply to the station, it is again floated onto
the d.c. bus bars with the help of FLOAT charger........
| Is This Answer Correct ? | 3 Yes | 0 No |
Why we use two wattmeter during block rotor test and no load test of 3phase induction motor? And how can we understand the neat power requirement of from this test?
A 200 KVA UPS's load current is 70 A. We want to provide a Generator back up. What capacity of DG required for this ?
I'm generating a pulse of 3V with frequency 80Hz (12.5ms time period) and pulse duration 0.125ms and feeding it to a transformer since i want the pulse to get amplified around 60V. At the output amplification s happening but the pulse is changed to a spike, can you tell me what could be the reason? (an ordinary transformer 220V-12V stepdown transformer is reverse connected ie. now it is 12V-220V stepup and voltage amplification happens)
How grounding is different than earthings?
why burdens of VTs is more than CTs?
Why slip ring ind. motor power consumption is low compare to induction motor .same 90 kw motor used same load output
What is oscillator circuit?
what is the harmonics.
What is the difference between Earthing and Neutral?
I want to give Power supply to a house from the Feeder, Total Load of the House is 128 KW, how to calculate cable size for this load ?
It is being often experienced that due to single phasing fault of any source transmission line of any closed loop synchronized circuit all the power transformers with primary stared trips but the power transformer with primary delta wont, why ?
how will you determine the short circuit capacity of a network
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)