What core magnetic balance test of transformer?
How to do this test in a three phase Star delta (star-LV,
Delta-HV) transformer?
How to measure and where to measure?
thanks and regards
Austin
Answers were Sorted based on User's Feedback
Answer / rajukumar sripelli
HI ,
this is rajukumar sripelli from REPUTED TRANSFORMER
MANUFACTURING COMPANY ..testing department ..
AS u all above is not fully correct....
Magnetic balance test is done on TRANSFORMER to see whether
the transformer core is magnetically balanced or
not...AND ALSO WINDING CONDITION....IN FAULT CONDITION DUE
TO HIGH CURRENTS WINDING MAY BE DAMAGE....
for example
we r having delta HV and star winding LV side ...
HV SIDE WE WIL BE HAVING THREE BUSHINGS....THOSE R 1U,1V,1W..
HV SIDE WE WIL BE HAVING FOUR BUSHINGS.....2U,2V,2W,2N...
WE CAN DO THIS MBT (MAGNETIC BALANCE TEST)WITH 1PHASE
SUPPLY(1PHASE AND NEUTRAL(230V)) OR WITH 2-PHASE
SUPPLY(2-PHASES(440V))
1ST STEP OF MBT: GIVE POWER SUPPLY 1-PHASE OR 2 PHASE
BETWEEN 1U AND 1V ,MEASURE THE VOLTAGES BETWEEN 1V-1W AND
1U-1W AND ALSO 2U-2N,2V-2N,2W-2N..
SO HERE IF THE CORE IS CORRECTLY BALANCED THEN WE WILL GET
RESULTS AS FOLLOWS
1U-1V 1V-1W 1U-1W 2U-2N 2V-2N 2W-2N
440 300 140 90 50 40
THAT MEANS HV SIDE : 1U-1V = 1V-1W + 1U-1W
I.E 440V = 300 + 140
AND ALSO LV SIDE : 2U-2N = 2V-2N + 2W-2N
90 = 50 + 40
STEP 2: AFTER DOING THIS ..INTERCHANGE THE CONNECTIONS
BETWEEN 1V-1W AND MEASURE THE VALUES AS ABOVE...
STEP 3: AFTER DOING THIS ..INTER CHANGE THE CONNECTIONS
BETWEEN 1U-1W AND MEASURE THE VALUES AS ABOVE...
IF ANY FAULT IS THERE IN TRANSFORMER WE CAN NOT FIND GOOD
RESULTS....
IF THE WINDING IS DAMAGED .... WE WILL GET ZERO VALUES ....
ex: HV SIDE 1U-1V = 1V-1W + 1U-1W
440V = 440 + 0
AND ALSO LV SIDE : 2U-2N = 2V-2N + 2W-2N
90 = 90 + 0
THIS IS THE ACTUAL APPLICATION OF MANGNETICA BALANCE TEST...
THANKS....
Is This Answer Correct ? | 287 Yes | 9 No |
Answer / engr. ziaul ashraf shafi
Answer #5 is fine.. but i want to add something more..
normally this test is made in star side of the transformer.
the result should be varified like following:
1) if 2u-2n is fed by 230 volt.
- the nearest phase (2v-2n) will experience the 85% to 90%
of fed voltage at 2u-2n. (i mean 2v-2n = 195.5 to 207
volt). And the distant phase (2w-2n) will experience the
10% to 15% of fed voltage at 2u-2n. (i mean 2w-2n = 23 to
34.5 volt).
2) if 2v-2n is fed by 230 volt.
- then the fed pahase is middle phase, and both other phase
are magnetically in equal distance.. so the measured
voltages in 2u-2n or 2w-2n = 50 % (or 40 to 60 % is also
accaptable). so the 2u-2n or 2w-2n = 92v to 138v is
accaptable.
3) if 2w-2n is fed by 230 volt.
- the nearest phase (2v-2n) will experience the 85% to 90%
of fed voltage at 2w-2n. (i mean 2v-2n = 195.5 to 207
volt). And the distant phase (2u-2n) will experience the
10% to 15% of fed voltage at 2u-2n. (i mean 2w-2n = 23 to
34.5 volt).
*If the results are found beyond these above mentioned
limits then other tests (like open ckt test with rated
voltage) should be performed to be sure about core and
winding.
*You can measure and note down the current of each injected
phase. it will give u a signaficant idea about winding. if
the winding has an inter-tern short then the faulty phase
will draw comapretively large magnetizing current like 3A
or 5A, wheather other phases will draw 60mA to 100mA.
*Remember, the magnetic reluctance path of a core is not
lenier, so the result veries itself. But big differences
are remarkable.
*Sometime due to non-lenier characteristic of magnatic
circuit and the presense of harmonics in the fluxes of un-
excited phases, the algebric sum of induced volage in two
phases may not be equal to the applied voltage.
*if there is a turn to turn fault in any phase winding, the
faulty section will draw comparetively large magnatizing
current which will oppose the magnetic fluxes and will
result a very low induced voltage (tends to zero) in the
faulty phase.
*this test should be performed after demagnaizing the
transformer properly. slightly magnatized transformer (like
after insulation test) can give you an unexpacted and
distorted result of magnetic balance test.
Is This Answer Correct ? | 73 Yes | 3 No |
MAGNETIC BALANCE TEST
THIS TEST IS SIMILAR AS OPEN CIRCUIT TEST
PROVIDE THE SINGLE PHASE SUPPLY (BELOW 230 V)TO THE STAR
SIDE OF THE TRANSFORMER BY PROPERLY CONNECTED
1.GIVE SUPPLY TO 2N AND 2U AND THEN MEASURE THE VOLTAGE ON
2N2V AND 2N2W
(i.e)IT SATISFIED THE CONDITION
2U2N=2V2N+2W2N
SIMILARILY THE TEST CONDUCTED ON OTHER TWO PHASES BY SAME
MEANS
(NOTE: NO ONE SHOULD BE STAND ON HIGH VOLTAGE SIDE WHILE
TESTING )
Is This Answer Correct ? | 100 Yes | 32 No |
Answer / krishna patil
What is the 2W 2V 2U 2N in transformer??
Is This Answer Correct ? | 37 Yes | 4 No |
Answer / mugaisi
Provide 2-phase supply on the HV side of transformer on two
phases.
Then measure magnetizing current in the supplied phases.
Then measure the voltages on the LV side.
Repeat the same for the other phases and measure current
and LV corresponding voltages.
The LV voltages should obey
ry = rb+by
and
rn = bn+yn
Is This Answer Correct ? | 39 Yes | 21 No |
Single phase Supply to 1U1V. 1V1W,1W1U
terminals turn by and induced voltage are mesured.
Meausered Voltage (v)
1U-1V 1V-1W w-1U 2N-2U 2N-2V 2N-2W
420 330 90 80 63 17
193 411 218 36 79 41
80 341 420 15 65 80
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / n. vajiravel
in case of star-delta trafo
if you apply single phase supply on primary 1u-1n then the
voltage should be divided to 1v-1n(70%) and 1w-1n(30%).
this result shows the correct magnetic coupling between the
windings.
example:
apply single phase supply to 1u-1n----100%(230v approx)
measure voltage in 1v-1n and 1w-1n then you will get
70% of 230V in 1v-1n and 30% of 230V in 1w-1n approximately.
apply single phase supply to 1v-1n-----100%(230v approx)
measure voltage in 1u-1n and 1w-1n then you will get 50% in
each.
apply single phase voltage to 1w-1n-----100%9230v approx)
measure voltage in 1u-1n and 1v-1n then you will get 30% of
230v in 1u-1n and 70% in 1v-1n approximately.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / johny
I MEASURED 100KVA TRANSFORMER DELTA/STAR AND I APLYED VOLTAGE
RY 390 YB-321+ BR-72.8
YB 390 RY-221+BR-168.3 ( THIS VOLTAGE FROM DG)
BR 390 RY-77.6+YB314.6
IS IT CORRECT? PLS GIVE ME REPLY
Is This Answer Correct ? | 8 Yes | 2 No |
Hi,
You may use either single-pase on the star side of the
transformer as in Answer #2 or apply two line voltages i.e.
apply 415V on A and B terminals on the HV-side of the
transformer and follow the steps of Rajukumar Sripelli in
Answer #5.
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / suresh sharma
ANSWER NO 5+9= is all the solution you required,
its me suresh sharma electrical PG IE ME ELEC.WORKING IN ONE
REPUTED FIRM OF TRANSFORMER
Is This Answer Correct ? | 5 Yes | 3 No |
how can we chacke adiod in a circuit
MCCB 400 Amps 50KA 430Volt AC What is mean by 50KA
how we calculate fault current& load factor or fault level&also the leakage current
Where the excitation is given either stator or rotor in actually in power plants?
What is the tipical Online UPS input voltage for 20 KVA load ( 3 Phase or 1 Phase )? Why ? Explain it...?
How to decrease or increase the range of voltmeter? can an ammeter be used to measure voltage? can a wattmeter used as voltmeter and ammeter?
give me the details of anti pumping relay
we have one oven for 12 zone we are installed ir lamp in oven we control load from thyrister and 0 to 5vdc so our zone no 8 getting bright in fraction of second so what we do.. Please answer
what can i do line to line fault
what is the main function of capacitors in mccs.
why maintain the Dg PF is 0.8? Explain?
as ac supply is given 2 the transformer why it doesnot depends upon powerfactor????