What core magnetic balance test of transformer?
How to do this test in a three phase Star delta (star-LV,
Delta-HV) transformer?
How to measure and where to measure?
thanks and regards
Austin
Answer Posted / e.saravanan
MAGNETIC BALANCE TEST
THIS TEST IS SIMILAR AS OPEN CIRCUIT TEST
PROVIDE THE SINGLE PHASE SUPPLY (BELOW 230 V)TO THE STAR
SIDE OF THE TRANSFORMER BY PROPERLY CONNECTED
1.GIVE SUPPLY TO 2N AND 2U AND THEN MEASURE THE VOLTAGE ON
2N2V AND 2N2W
(i.e)IT SATISFIED THE CONDITION
2U2N=2V2N+2W2N
SIMILARILY THE TEST CONDUCTED ON OTHER TWO PHASES BY SAME
MEANS
(NOTE: NO ONE SHOULD BE STAND ON HIGH VOLTAGE SIDE WHILE
TESTING )
| Is This Answer Correct ? | 100 Yes | 32 No |
Post New Answer View All Answers
state types of reflectors in illumination engg. ???????
What must be the minimum distance maintained between 2 Generators as per International standards?
What is Diff btw Fire Alarm & VESDA System???
How energy is generated in hydroelectric power plant?
What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?
What is the use of bundle conductors?
what is the difference between unarmoured & Flexible cable? How to identified?
How will calculate losses in an multi core Aluminium LT cable of different sizes & upto what length we can use a LT Cable ?
as a electrical student why should i hire you?
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
What is meant by coupling capacitor?
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
Define load factor?
why ct ,cvt should be stored in a vertical position?
Explain (in simple ) - root mean square. whats its role in electrical fundamandal.where its used