What core magnetic balance test of transformer?
How to do this test in a three phase Star delta (star-LV,
Delta-HV) transformer?
How to measure and where to measure?
thanks and regards
Austin
Answer Posted / e.saravanan
MAGNETIC BALANCE TEST
THIS TEST IS SIMILAR AS OPEN CIRCUIT TEST
PROVIDE THE SINGLE PHASE SUPPLY (BELOW 230 V)TO THE STAR
SIDE OF THE TRANSFORMER BY PROPERLY CONNECTED
1.GIVE SUPPLY TO 2N AND 2U AND THEN MEASURE THE VOLTAGE ON
2N2V AND 2N2W
(i.e)IT SATISFIED THE CONDITION
2U2N=2V2N+2W2N
SIMILARILY THE TEST CONDUCTED ON OTHER TWO PHASES BY SAME
MEANS
(NOTE: NO ONE SHOULD BE STAND ON HIGH VOLTAGE SIDE WHILE
TESTING )
| Is This Answer Correct ? | 100 Yes | 32 No |
Post New Answer View All Answers
On a 3 winding transformer YNynd11, how do you apply REF protection to the Delta tertiary winding that is supplying auxiliaries to a substation?
What is FM200 Gas??Applications........
What is current divider rule (cdr)?
When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?
What are test signals and their significance?
The slip during plugging operation is given by= A 1-s B 2+s C 1+s D 2-s
WHAT IS DEAD END IN PROTECTION?
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?
what is Anti-pumping?
What is DC series motor?
How impulse levels are calculated that for 11kV impulse is 75kvp, for 24kV impulse is 125kvp ?
Why Transformer Neutral having one earth pit ( more earth electrode resistance) whereas body have many earth pit ( less earth electrode resistance)?
what is the difference b/w UHVDC and HVDC(LIGHT)?
Is there any specialised book to refer about fault level calculation both in MV and LV side??
When a square wave is applied to primary of a transformer then what will be output wave form of secondary ?