Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

What core magnetic balance test of transformer?
How to do this test in a three phase Star delta (star-LV,
Delta-HV) transformer?
How to measure and where to measure?

thanks and regards
Austin

Answer Posted / engr. ziaul ashraf shafi

Answer #5 is fine.. but i want to add something more..
normally this test is made in star side of the transformer.
the result should be varified like following:
1) if 2u-2n is fed by 230 volt.
- the nearest phase (2v-2n) will experience the 85% to 90%
of fed voltage at 2u-2n. (i mean 2v-2n = 195.5 to 207
volt). And the distant phase (2w-2n) will experience the
10% to 15% of fed voltage at 2u-2n. (i mean 2w-2n = 23 to
34.5 volt).
2) if 2v-2n is fed by 230 volt.
- then the fed pahase is middle phase, and both other phase
are magnetically in equal distance.. so the measured
voltages in 2u-2n or 2w-2n = 50 % (or 40 to 60 % is also
accaptable). so the 2u-2n or 2w-2n = 92v to 138v is
accaptable.
3) if 2w-2n is fed by 230 volt.
- the nearest phase (2v-2n) will experience the 85% to 90%
of fed voltage at 2w-2n. (i mean 2v-2n = 195.5 to 207
volt). And the distant phase (2u-2n) will experience the
10% to 15% of fed voltage at 2u-2n. (i mean 2w-2n = 23 to
34.5 volt).

*If the results are found beyond these above mentioned
limits then other tests (like open ckt test with rated
voltage) should be performed to be sure about core and
winding.
*You can measure and note down the current of each injected
phase. it will give u a signaficant idea about winding. if
the winding has an inter-tern short then the faulty phase
will draw comapretively large magnetizing current like 3A
or 5A, wheather other phases will draw 60mA to 100mA.
*Remember, the magnetic reluctance path of a core is not
lenier, so the result veries itself. But big differences
are remarkable.
*Sometime due to non-lenier characteristic of magnatic
circuit and the presense of harmonics in the fluxes of un-
excited phases, the algebric sum of induced volage in two
phases may not be equal to the applied voltage.
*if there is a turn to turn fault in any phase winding, the
faulty section will draw comparetively large magnatizing
current which will oppose the magnetic fluxes and will
result a very low induced voltage (tends to zero) in the
faulty phase.
*this test should be performed after demagnaizing the
transformer properly. slightly magnatized transformer (like
after insulation test) can give you an unexpacted and
distorted result of magnetic balance test.

Is This Answer Correct ?    73 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how does an centrifugal and screw type chiller will work. which chiller efficiency is high and why.

2289


Pl.brief me any electrical major fault you have rectified.

1959


What are gain margin and phase margin?

1384


hi guys please tell me the procedure for mesuring the coil resistance of 3ph induction motor?

1897


if 12v battery get discharged for 2 months after if we put charge it will charge again?how much time it will take to charge?

1927


number of I/O devices in siemense plc

2139


what is the formula for calculating the phase clerance between two phases and phase to earth how to calculate the cable for a motor

2020


placement paper samples of mspl company

1942


What is the difference between isolators and electrical circuit breakers?

1184


How to select a cable size for particular load?

1828


Explain (in simple ) - root mean square. whats its role in electrical fundamandal.where its used

2392


For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?

2105


what is frequency response?

1143


what is the transformer turn ratio formula and give some examples?

2428


How to work E.L.C.B and how to connect in circuit.

2014