What is the recommended voltage gap between Live and Earth
and ,Earth and Neutral.If these are exceded what is the
solution.
Answers were Sorted based on User's Feedback
L.E=230 v(If single phase),
=440 v(If three phase),
E.N=1.7 v(If proper earthing),
=2 v(Acceptable),
If these are exceded concentrat on earthing.Maintain earth
resistance is <1 omh.
| Is This Answer Correct ? | 20 Yes | 0 No |
If the neutral of the system is earthed then the voltage
between Live condutor and earth is line voltage/ squre root
of 3.i.e, 415 volts is L-L voltage then the voltage L - E
is 239 volts.
Voltage between Neutral and earth should not exceed 5
volts.if it exceeds the earthing was not proper. needs
attention on earthing.
| Is This Answer Correct ? | 15 Yes | 2 No |
it is possible to measurement of tension of slipring induction motor(SRIM)carbon brushes, any maesuring instruments are available in the markets.
which capacity of RCCB used for five thousand watt electricity load?
What is electrical cable termination
what is AMF panel????????
Why the wave trap is put in Y phse only in switchyard?why not in other phases?
what are the difference between protection class CT and Class PS CT
Why power factor should not be in leading (capacitive) mode of any load.
what is bausbar?
how we select fuse rating for motor?
Work done in a free expansion process is
define hysteresis loss, eddy current loss and windage loss
to transmit 30kw of power at 30 km what is voltage required
2 Answers Anglo Eastern, Merchant Navy, NPCIL,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)