For testing 33kv cable hipot testing. How much kv we have to
Apply .Give in details.
Answers were Sorted based on User's Feedback
Answer / zahid ali
2E + 1 KV = 67 KV DC Hi pot
67 * .707 = 47 KV AC Hi pot
| Is This Answer Correct ? | 119 Yes | 58 No |
Answer / bapi
AS HI POT TEST IS CONDUCTED IN DC SO APPROX. 1.5 TIMES OF
AC SUPPLY VOLTAGE IS APPLIED FOR 1 MINUTE.
FOR 33 kV CABLE APPROX. 50kV FOR 1 MINUTE WILL BE APPLIED.
FOR TESTING OF "R" PHASE WE HAVE TO SHORT "Y" AND "B" PHASE
ALONG WITH ARMOUR & IT SHOULD BE EARTHED. SIMILARLY FOR Y &
B PHASE.
AFTER EACH PHASE TESTING IT SHOULD BE DISCHARGED THROUGH
DISCHARGE RODS.
| Is This Answer Correct ? | 66 Yes | 30 No |
Answer / s.jeganath
(2E+1)1.414=dc
2E+1 =AC
(2*33000+1)1.414=DC
67000*1.414=DC
94738v=DC (it is a 100%)
but apply in 80% only it is standard for 33kv cable
APPly voltage dc=94738*0.8=75790V
(75.790KV DC)
| Is This Answer Correct ? | 43 Yes | 18 No |
Answer / mathiraja
2E+1KV=67KV FOR AC VOLTS
(2E+1KV)*1.414=94.73KV FOR DC VOLTS
ACCORDING TO IEC60950 STANDARDS.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / manikandan n
For DC Hipot test the applied voltage calculating formula is equal to (2E+1000)*1.414*(80/100)
E = system voltage
1.414 = For DC RMS conversion.
80% = test conduct in site at second time.
| Is This Answer Correct ? | 19 Yes | 4 No |
Answer / ram sundar
For DC HIPOT = 1.414*(2E+1)
E=33/1.73=19.07
DC Hipot = 1.414*(2*19.07+1)
55.34kv approx 56Kv
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / sunil choudhary
FOR TESTING 6.6KV CABLE HIPOT TESTING.HOW MUCH KV WE HAVE
TO
APPLY .GIVE IN DETAILS.
sunil choudhary
| Is This Answer Correct ? | 20 Yes | 15 No |
Answer / yousaf
D.C. voltage equal to 3 x U0 shall be applied for 15 minutes. The standard is 1EC5840.
57KV FOR 15 MIN.
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / jim sreedharan
For 33 KV cables we do three tests.
1. Vlf Test: We apply 10 kv dc between graphite and armour
at a low frequency (normally between 0.02 hz to 0.05 hz)
for 1 hour.
2. Insulation Resistance :- We apply 5 kv dc for 1 min
3. High Voltage ac Test:- We apply 57.1 kv for 30 mins
(33/1.732)x 3 = 57.1 kv
God Bless
| Is This Answer Correct ? | 12 Yes | 9 No |
Answer / jayasanker
33KV CABLE
FORMULA:2E+1*1.414
2*33+1*1.414 = 94KV DC
IF BUS BAR 2*33+1 = 67KV AC
| Is This Answer Correct ? | 8 Yes | 5 No |
Isolation transformer primary to sec turns ratio?
Differnce between Analog & Digital
what is impedence of transformer? its formula
what is the advantage and disadvantage of billing in kwh and kvah by electricity board .
Do power transformers have an Automatic Voltage Regulator (AVR) just like the alternator/generator in a power system?
how to find the resistance
how many stairs have you climbed while you were coming
What is the difference between eath fault protection & Restricted Earth fault Protection?
i applied for the ap transco please forward the freqventley asked QA
According to ohms law voltage proportional to current, then why should current rating is low with high voltage rating in transformer?
What will be the direction of rotation of a Alternator in case it goes in motoring action when connected with grid ?
why we are discharging h.t supply during shutdown time
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)