For testing 33kv cable hipot testing. How much kv we have to
Apply .Give in details.
Answers were Sorted based on User's Feedback
Answer / zahid ali
2E + 1 KV = 67 KV DC Hi pot
67 * .707 = 47 KV AC Hi pot
| Is This Answer Correct ? | 119 Yes | 58 No |
Answer / bapi
AS HI POT TEST IS CONDUCTED IN DC SO APPROX. 1.5 TIMES OF
AC SUPPLY VOLTAGE IS APPLIED FOR 1 MINUTE.
FOR 33 kV CABLE APPROX. 50kV FOR 1 MINUTE WILL BE APPLIED.
FOR TESTING OF "R" PHASE WE HAVE TO SHORT "Y" AND "B" PHASE
ALONG WITH ARMOUR & IT SHOULD BE EARTHED. SIMILARLY FOR Y &
B PHASE.
AFTER EACH PHASE TESTING IT SHOULD BE DISCHARGED THROUGH
DISCHARGE RODS.
| Is This Answer Correct ? | 66 Yes | 30 No |
Answer / s.jeganath
(2E+1)1.414=dc
2E+1 =AC
(2*33000+1)1.414=DC
67000*1.414=DC
94738v=DC (it is a 100%)
but apply in 80% only it is standard for 33kv cable
APPly voltage dc=94738*0.8=75790V
(75.790KV DC)
| Is This Answer Correct ? | 43 Yes | 18 No |
Answer / mathiraja
2E+1KV=67KV FOR AC VOLTS
(2E+1KV)*1.414=94.73KV FOR DC VOLTS
ACCORDING TO IEC60950 STANDARDS.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / manikandan n
For DC Hipot test the applied voltage calculating formula is equal to (2E+1000)*1.414*(80/100)
E = system voltage
1.414 = For DC RMS conversion.
80% = test conduct in site at second time.
| Is This Answer Correct ? | 19 Yes | 4 No |
Answer / ram sundar
For DC HIPOT = 1.414*(2E+1)
E=33/1.73=19.07
DC Hipot = 1.414*(2*19.07+1)
55.34kv approx 56Kv
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / sunil choudhary
FOR TESTING 6.6KV CABLE HIPOT TESTING.HOW MUCH KV WE HAVE
TO
APPLY .GIVE IN DETAILS.
sunil choudhary
| Is This Answer Correct ? | 20 Yes | 15 No |
Answer / yousaf
D.C. voltage equal to 3 x U0 shall be applied for 15 minutes. The standard is 1EC5840.
57KV FOR 15 MIN.
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / jim sreedharan
For 33 KV cables we do three tests.
1. Vlf Test: We apply 10 kv dc between graphite and armour
at a low frequency (normally between 0.02 hz to 0.05 hz)
for 1 hour.
2. Insulation Resistance :- We apply 5 kv dc for 1 min
3. High Voltage ac Test:- We apply 57.1 kv for 30 mins
(33/1.732)x 3 = 57.1 kv
God Bless
| Is This Answer Correct ? | 12 Yes | 9 No |
Answer / jayasanker
33KV CABLE
FORMULA:2E+1*1.414
2*33+1*1.414 = 94KV DC
IF BUS BAR 2*33+1 = 67KV AC
| Is This Answer Correct ? | 8 Yes | 5 No |
what is the range of thermal overload and over current. Answer should be in percentage of current.
what is basically a pulse transformer?
what is the location of lighting switch of battery room
when a machine act as genartor and as motor?
HOW TO IDENTIFY THE RELAYS WHICH APPLICATION IN WHICH RELAY USING?
DG SET BLOCK DIGRAM
What type of core material is used for metering C.T and protection C.T???
What is application of MCB & How it works
relation between power station capacity and voltage level?
What is Auto Mains Failure Panel & Auto Synchronizing Panel
Hi,My name is ranms i want to know the machine vibration related problems.post me if any body knows. 1) Possible causes of machine horizontal vibration high? 2) Possible causes of machine vertical vibration high? 3) Possible causes of machine axial vibration high?
How to select batteries required for ups and the inverter if we Known load? And how AH is selected of battery?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)