For testing 33kv cable hipot testing. How much kv we have to
Apply .Give in details.
Answers were Sorted based on User's Feedback
Answer / dhanraj
For 33 Kv cable DC hi pot test can be done like (2*E+1)1.414
here E=Voltage , 1.414 is the root 2 value.
Now (2*33+1)=67Kv
Then 67*1.414=94.738 Kv this is 100% of cable test.
In manufacturing factory they will test up to 80% of the voltage in that 100% (94.73*0.8)=75.79 Kv.
But in consumer side they will test up to 80% of voltage that injected in the factory voltage (75.79*0.8)=60.64 Kv.
Now 60.64 Kv is apply for 3 mins maximum.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / michael aliganga
CABLE FACTORY AC TEST VOLTAGE =2E+1kV= 2X35+1= 71kV
DC HIPOT TEST:
CABLE INSTALLATION TEST DURING AND AFTER = ET= EF X 1.8 X 0.8
ET = 71 X 1.8 X 0.8 = 102kV, ICEA DC FIELD TEST VOLTAGE
(ICEA S-97-682) IS 100 kV FOR 35 KV SHIELDED POWER CABLE.
EF=CABLE MANUFACTURERS RECOMMENDED FACTORY AC TEST VOLTAGE
IF NOT AVAIABLE USE 2E+1KV
1.8 AC TO DC CONVERSION FACTOR (QUITE COMMON)
0.8 CONVERSION FACTOR FOR DERATING FROM FACTORY TESTING TO
ACCEPTANCE TESTING.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / manohar
Hipot test conduct for 33kV cable is 1.5 times of rating
voltage in DC(49kV approx will be apply for 1 minute.)
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / martin thomas
Iec code
Ac= (2 x e) 1
Dc={(2 x e) 1} x 1.414
1.414=sqrt (2)
E= rated voltage
Aramco std
Dc =4 x u
U= phase voltage
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.shiva krishna
AC Hipot test voltage = Nominal input voltage * 2 + 1000
DC Hipot test voltage = AC Hipot test voltage * 1.414
for 33kv
ac hipot v/g = 33000*2+1000 = 67kv
dc hipot v/g = 67000 * 1.414 = 95kv
Is This Answer Correct ? | 16 Yes | 25 No |
Answer / raveendra
(2E+1)=67 kV FOR AC HIPOT ( 1 minute test)
67*1.7 = 113.9 DC HIPOT ( i minute test)
for aged cables generally we will apply 65% of the above
Is This Answer Correct ? | 24 Yes | 37 No |
Answer / sharafuddeen
AS PER IEEE 400.1 ,THE DC TEST VOLTAGE SHOULD BE 100KV FOR
A 35 KV CABLES.AND THERE IS NO A PARTICULAR FORMULA TO
CALCULATE THE TEST VOLTAGE.IT SHOULD BE AS PER THE
STANDARDS AS PER WHICH THE CABLES MANUFACURED.
Is This Answer Correct ? | 9 Yes | 25 No |
TRANAFORMER RATING 500 KVA,33KV/433, SECONDARY SIDE SWITCHED ON ONLY CAPACITOR LOAD 140 AMS, PRIMARY SIDE HOW MUCH VOLTS INCREASE?
what convarts RRA in alternator ,AC to DC or DC to AC,
Name one of major transformer company in KSA ?
What is the power factor of a transformer at no load?
DRAW THE DIFFERENCE BETWEEN GROUND AND NEUTRAL IN BOTH SINGLE PHASE AND THREE PHASE?
in india why 50 hz and 220 volt taken as standard rating for equipments whereas in US 100hz and 110v is consided as standard rating.is this method save power.
WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??
I HAVE A 50A MCCB AS PER DESIGN LINE WIRE CONNECT UPWORD SIDE AND LOAD IS CONNECTED TO DOWNWARD SIDE TO THE MCCB.IF NOW ANY ONE CHANGE SUPPLY & LOAD(WISEVERSA) WHAT HAPPENS ? DOES MCCB OPERATION OR WORKING FUNCTION NORMAL IF YES THAN WHY THERE ARE MARKED LINE & LOAD ON MCCB.
WHAT IS THE DIFFERENCE BETWEEN GENERAL INVERTER AND SOLOR INVERTER TELL ME PLZ
why are you use the crgo core lamination in transformer
which will glow brighter?bulb 1 (110v,100w) and bulb 2 (230v.200w) series connection
1.What is the maximum transmission voltage in india & where it is located? 2.more information about indian power scenario.