For testing 33kv cable hipot testing. How much kv we have to
Apply .Give in details.

Answers were Sorted based on User's Feedback



For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / rajan

U0 * 4 = 33/ 1.732

= 19.05 * 4
= 76KV

Is This Answer Correct ?    33 Yes 31 No

For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / dhanraj

For 33 Kv cable DC hi pot test can be done like (2*E+1)1.414
here E=Voltage , 1.414 is the root 2 value.
Now (2*33+1)=67Kv
Then 67*1.414=94.738 Kv this is 100% of cable test.
In manufacturing factory they will test up to 80% of the voltage in that 100% (94.73*0.8)=75.79 Kv.
But in consumer side they will test up to 80% of voltage that injected in the factory voltage (75.79*0.8)=60.64 Kv.
Now 60.64 Kv is apply for 3 mins maximum.

Is This Answer Correct ?    2 Yes 0 No

For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / michael aliganga

CABLE FACTORY AC TEST VOLTAGE =2E+1kV= 2X35+1= 71kV
DC HIPOT TEST:
CABLE INSTALLATION TEST DURING AND AFTER = ET= EF X 1.8 X 0.8
ET = 71 X 1.8 X 0.8 = 102kV, ICEA DC FIELD TEST VOLTAGE
(ICEA S-97-682) IS 100 kV FOR 35 KV SHIELDED POWER CABLE.

EF=CABLE MANUFACTURERS RECOMMENDED FACTORY AC TEST VOLTAGE
IF NOT AVAIABLE USE 2E+1KV
1.8 AC TO DC CONVERSION FACTOR (QUITE COMMON)
0.8 CONVERSION FACTOR FOR DERATING FROM FACTORY TESTING TO
ACCEPTANCE TESTING.

Is This Answer Correct ?    3 Yes 2 No

For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / manohar

Hipot test conduct for 33kV cable is 1.5 times of rating
voltage in DC(49kV approx will be apply for 1 minute.)

Is This Answer Correct ?    4 Yes 4 No

For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / martin thomas

Iec code
Ac= (2 x e) 1
Dc={(2 x e) 1} x 1.414
1.414=sqrt (2)
E= rated voltage

Aramco std

Dc =4 x u
U= phase voltage

Is This Answer Correct ?    0 Yes 0 No

For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / b.gusain

Uo X 4 as per ICE

Is This Answer Correct ?    0 Yes 0 No

For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / chandan gupta

75.790 kv dc

Is This Answer Correct ?    3 Yes 5 No

For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / a.shiva krishna

AC Hipot test voltage = Nominal input voltage * 2 + 1000
DC Hipot test voltage = AC Hipot test voltage * 1.414
for 33kv
ac hipot v/g = 33000*2+1000 = 67kv
dc hipot v/g = 67000 * 1.414 = 95kv

Is This Answer Correct ?    16 Yes 25 No

For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / raveendra

(2E+1)=67 kV FOR AC HIPOT ( 1 minute test)
67*1.7 = 113.9 DC HIPOT ( i minute test)

for aged cables generally we will apply 65% of the above

Is This Answer Correct ?    24 Yes 37 No

For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details...

Answer / sharafuddeen

AS PER IEEE 400.1 ,THE DC TEST VOLTAGE SHOULD BE 100KV FOR
A 35 KV CABLES.AND THERE IS NO A PARTICULAR FORMULA TO
CALCULATE THE TEST VOLTAGE.IT SHOULD BE AS PER THE
STANDARDS AS PER WHICH THE CABLES MANUFACURED.

Is This Answer Correct ?    9 Yes 25 No

Post New Answer

More Electrical Engineering Interview Questions

TRANAFORMER RATING 500 KVA,33KV/433, SECONDARY SIDE SWITCHED ON ONLY CAPACITOR LOAD 140 AMS, PRIMARY SIDE HOW MUCH VOLTS INCREASE?

1 Answers   BPL,


what convarts RRA in alternator ,AC to DC or DC to AC,

1 Answers   Birla,


Name one of major transformer company in KSA ?

0 Answers  


What is the power factor of a transformer at no load?

0 Answers  


DRAW THE DIFFERENCE BETWEEN GROUND AND NEUTRAL IN BOTH SINGLE PHASE AND THREE PHASE?

2 Answers  






in india why 50 hz and 220 volt taken as standard rating for equipments whereas in US 100hz and 110v is consided as standard rating.is this method save power.

5 Answers   Wipro,


WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??

0 Answers   Teil,


I HAVE A 50A MCCB AS PER DESIGN LINE WIRE CONNECT UPWORD SIDE AND LOAD IS CONNECTED TO DOWNWARD SIDE TO THE MCCB.IF NOW ANY ONE CHANGE SUPPLY & LOAD(WISEVERSA) WHAT HAPPENS ? DOES MCCB OPERATION OR WORKING FUNCTION NORMAL IF YES THAN WHY THERE ARE MARKED LINE & LOAD ON MCCB.

0 Answers   HCL, TCS,


WHAT IS THE DIFFERENCE BETWEEN GENERAL INVERTER AND SOLOR INVERTER TELL ME PLZ

0 Answers   Epcon,


why are you use the crgo core lamination in transformer

6 Answers  


which will glow brighter?bulb 1 (110v,100w) and bulb 2 (230v.200w) series connection

6 Answers   EnPower India,


1.What is the maximum transmission voltage in india & where it is located? 2.more information about indian power scenario.

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)