For testing 33kv cable hipot testing. How much kv we have to
Apply .Give in details.
Answers were Sorted based on User's Feedback
Answer / dhanraj
For 33 Kv cable DC hi pot test can be done like (2*E+1)1.414
here E=Voltage , 1.414 is the root 2 value.
Now (2*33+1)=67Kv
Then 67*1.414=94.738 Kv this is 100% of cable test.
In manufacturing factory they will test up to 80% of the voltage in that 100% (94.73*0.8)=75.79 Kv.
But in consumer side they will test up to 80% of voltage that injected in the factory voltage (75.79*0.8)=60.64 Kv.
Now 60.64 Kv is apply for 3 mins maximum.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / michael aliganga
CABLE FACTORY AC TEST VOLTAGE =2E+1kV= 2X35+1= 71kV
DC HIPOT TEST:
CABLE INSTALLATION TEST DURING AND AFTER = ET= EF X 1.8 X 0.8
ET = 71 X 1.8 X 0.8 = 102kV, ICEA DC FIELD TEST VOLTAGE
(ICEA S-97-682) IS 100 kV FOR 35 KV SHIELDED POWER CABLE.
EF=CABLE MANUFACTURERS RECOMMENDED FACTORY AC TEST VOLTAGE
IF NOT AVAIABLE USE 2E+1KV
1.8 AC TO DC CONVERSION FACTOR (QUITE COMMON)
0.8 CONVERSION FACTOR FOR DERATING FROM FACTORY TESTING TO
ACCEPTANCE TESTING.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / manohar
Hipot test conduct for 33kV cable is 1.5 times of rating
voltage in DC(49kV approx will be apply for 1 minute.)
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / martin thomas
Iec code
Ac= (2 x e) 1
Dc={(2 x e) 1} x 1.414
1.414=sqrt (2)
E= rated voltage
Aramco std
Dc =4 x u
U= phase voltage
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jagan
33kV cable hipot Test
33*2+1=67
67/√3=38.68 for single cable
38.68*√2=57.8 for diode dc convert RMS
57.8*0.8=46.3 for dielectric % reduce by year
Finally apply new cable 46.3KV /phase
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.shiva krishna
AC Hipot test voltage = Nominal input voltage * 2 + 1000
DC Hipot test voltage = AC Hipot test voltage * 1.414
for 33kv
ac hipot v/g = 33000*2+1000 = 67kv
dc hipot v/g = 67000 * 1.414 = 95kv
| Is This Answer Correct ? | 16 Yes | 25 No |
Answer / raveendra
(2E+1)=67 kV FOR AC HIPOT ( 1 minute test)
67*1.7 = 113.9 DC HIPOT ( i minute test)
for aged cables generally we will apply 65% of the above
| Is This Answer Correct ? | 24 Yes | 37 No |
I If i have 2kv ups in which 38Amp *8battries hou many hour's back up i get from 600Watts
What is servo motor? what is its purpose?
i am swathi, b.tech 4th year. In smps(switched mode power supply)we are using diodes,mosfets,igbts for controling of current. And my question is why we did not use thyristors(scr)? it is also act as a switch,then what is the drawback of scr as compared to above transisters> if we use the scr,then what is happening ? plz give reply as soon as possible bcoz i am doing project on smps. plz frnds i want ans for that. if anybody know the ans plz send to my e-mail id /swathi.tadakapally@gmail.com/
can any tell me why slope 40% and 80% is calculated in differential protection?
WHY IL=IPH IN STAR AND WHY IPH=IL/1.732 IN DELTA? WHAT IS REASON BEHIND IT?
Explain about 3 phase motor fault current calculation with examples?
HT/LT TRANSFORMER TEST?
what is the instrument used for measuring insulator RESISTANCE
why only 11kv level is used for transmission purpose? why not 230v?
What is the difference between amorphous core transformer and CRGO core transformer?.
A 11KV, 1200 A breaker combination fixed in a cubicle for HT motor.Is normally for 11 KV motor fuse is using? if Yes, What range fuse is required?
Under wat condition statcom operates as an inductor for the transmission line?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)