For testing 33kv cable hipot testing. How much kv we have to
Apply .Give in details.
Answers were Sorted based on User's Feedback
Answer / dhanraj
For 33 Kv cable DC hi pot test can be done like (2*E+1)1.414
here E=Voltage , 1.414 is the root 2 value.
Now (2*33+1)=67Kv
Then 67*1.414=94.738 Kv this is 100% of cable test.
In manufacturing factory they will test up to 80% of the voltage in that 100% (94.73*0.8)=75.79 Kv.
But in consumer side they will test up to 80% of voltage that injected in the factory voltage (75.79*0.8)=60.64 Kv.
Now 60.64 Kv is apply for 3 mins maximum.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / michael aliganga
CABLE FACTORY AC TEST VOLTAGE =2E+1kV= 2X35+1= 71kV
DC HIPOT TEST:
CABLE INSTALLATION TEST DURING AND AFTER = ET= EF X 1.8 X 0.8
ET = 71 X 1.8 X 0.8 = 102kV, ICEA DC FIELD TEST VOLTAGE
(ICEA S-97-682) IS 100 kV FOR 35 KV SHIELDED POWER CABLE.
EF=CABLE MANUFACTURERS RECOMMENDED FACTORY AC TEST VOLTAGE
IF NOT AVAIABLE USE 2E+1KV
1.8 AC TO DC CONVERSION FACTOR (QUITE COMMON)
0.8 CONVERSION FACTOR FOR DERATING FROM FACTORY TESTING TO
ACCEPTANCE TESTING.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / manohar
Hipot test conduct for 33kV cable is 1.5 times of rating
voltage in DC(49kV approx will be apply for 1 minute.)
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / martin thomas
Iec code
Ac= (2 x e) 1
Dc={(2 x e) 1} x 1.414
1.414=sqrt (2)
E= rated voltage
Aramco std
Dc =4 x u
U= phase voltage
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jagan
33kV cable hipot Test
33*2+1=67
67/√3=38.68 for single cable
38.68*√2=57.8 for diode dc convert RMS
57.8*0.8=46.3 for dielectric % reduce by year
Finally apply new cable 46.3KV /phase
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.shiva krishna
AC Hipot test voltage = Nominal input voltage * 2 + 1000
DC Hipot test voltage = AC Hipot test voltage * 1.414
for 33kv
ac hipot v/g = 33000*2+1000 = 67kv
dc hipot v/g = 67000 * 1.414 = 95kv
| Is This Answer Correct ? | 16 Yes | 25 No |
Answer / raveendra
(2E+1)=67 kV FOR AC HIPOT ( 1 minute test)
67*1.7 = 113.9 DC HIPOT ( i minute test)
for aged cables generally we will apply 65% of the above
| Is This Answer Correct ? | 24 Yes | 37 No |
Is there any difference between load based power plant and coal based power plant?
how to calculate current in HT side when we having LT current
What technology is used in latest generators?
why+ve is earthed in electrostatic precipitator in thermal power plant
Write the Name of 7 Birsrestho of Bangladesh with their designation
why does rotor rotets?
Can we check ELCB constantly from R1 to R8 phase in 1 no DB?
What is the actual meaning of thermal power efficiency ?
Is there any Institution for giving M-tech in Electrical engineering for those who r in service? Give the details please.
what is difference b/w squirrel cage rotor and wound rotor
How we calculate DC inducation moter Amp? Sir pls give me formula......
Difference between ups and invertor
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)