For testing 33kv cable hipot testing. How much kv we have to
Apply .Give in details.
Answer Posted / mathiraja
2E+1KV=67KV FOR AC VOLTS
(2E+1KV)*1.414=94.73KV FOR DC VOLTS
ACCORDING TO IEC60950 STANDARDS.
| Is This Answer Correct ? | 22 Yes | 2 No |
Post New Answer View All Answers
is it possible to have dc motors on single chip
can we use ZNyn11 transformer instead of Dyn11 transformer in distribution for effectively eliminating harmonics from the industrial loads.
How we select the vector group of 3phase power transformer?
when will be the iocl interview results i faced interview on 8th september 2008 iam from electrical branch i faced interview for the post of electrical engineer??????????????????????//
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
what will happen if i connect 12 volt battery with 24 volt battery charger.
WHAT IS THE PARTIAL DISCHARGE TEST?
how to select fuse rating for a 3-phase motor ???
What is the drawback of static coefficients?
what is the difference between c power and U power acb breaker
What is the meaning of HT Trivector Meter ?
what is the minimum winding resistance of 30hp compressor, to run or to switch on
How to check the thermocouple is correctly connected to cable for K type? (i,e positive pole is connected to non magnetic conductor and negative pole is connected to magnetic conductor)
which is the most advanced form of SF6 BREAKER?Can we use other gases to quench the arc?
Give some differences between open loop and closed loop?