Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


generaly all power generating devices is expressed in KVA
or MVA then why power ststion is expressed in MW

Answers were Sorted based on User's Feedback



generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / anubis

KVA or MVA is used to measure apparent power. MW is used
for real power. Since the resistance and reactance for a
generating device is known, the apparent power can be
calculated. For the power station the apparent power will
not only depend upon the internal impedence of the station,
and the wies, but also upon the grid. This is not a fixed
number and varies with conditions, thus making it
impossible to judge. Thus it is safer to just give the real
power and then calculate th apparent power depending upon
the load used.

Is This Answer Correct ?    16 Yes 1 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / b.prakash.

KVA meanas apparent power it depends on power factor if
power factor is high the efficiency of system also high.
But in MW it true power means (load) if u r using a 2kw
heater then it will consume 2 kw. but in KVA suppose for ex.
transformer capacity is 1000kva & PF is 0.8 means we can
use only 80% of the total kva & it depends on the load also
that which type of load u r using. if u r using, capacitive
load or resistance load then the PF will be high. But if u
r using Inductive load then the PF will be less.

Is This Answer Correct ?    6 Yes 1 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / nikunj thakkar

the basic reason behind this question is that all the power station are heaving there reactive and active power delivering capacity so they are specifying that maximum power that can be delivered by company is in MW

Is This Answer Correct ?    2 Yes 0 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / kishore

IT IS BECOZ POWER STATION RATING INCLUDES
EFFICIENCY/RATING OF ALTERNATOR AS WELL AS TURBINE.

Is This Answer Correct ?    5 Yes 6 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / jeet

Generally our devices losses only depends on voltage and current it does not includes P.f so we take there ratings in MVA or KVA but in power house the power generated and transmitted is depends on P.f also along with V and I.Therefore we keep rating of power house in Kw and aplliences in KVA or MVA.

Is This Answer Correct ?    0 Yes 1 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / ynrao

Along with MW the rated PF also given on name plate of Gen
to display the optimum loading. That means at that PF the
rating is __ MW.

Is This Answer Correct ?    1 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between neutral

10 Answers  


what is the full Form of AAC ant conductor?

5 Answers  


At 765Kv, I have seen the use of PT at line side for metering and CVT for protection, although as far as my knowledge is concern, PT at this voltage level will have huge loss and more cost as compared to CVT as CVT can also perform same function of Protection and Metering? So my question is why use PT and not CVT for metering and protection in order to reduce the cost.

1 Answers  


On what basis no of earth pits are to be decided either for transformers or for equipment?

8 Answers   BEL, Reliance,


why insulators colour is BROWN?

1 Answers  


my motor rating is 800HP, 128Amps, 3.3kV. What is capaitor bank i can use for PF improvement to 0.990?

3 Answers  


After synchronizing the running generator with grid, the avr getting tripped and the generator breaker also oettong tripped, before tripping the avr the pf meter of generator is showing leading pf please kindly give a suggestion to rectify this problem.

2 Answers   Thermax,


What is the Different Between Breaker and One and half breaker.

2 Answers  


What is the difference between an ELCB and a RCD?

2 Answers   Schneider,


Sir Power transformer :- (in generating station) Alternator terminals side - Delta HT transmission line side - Star Why?

4 Answers   Kirloskar,


What is WLD System????

3 Answers   Emerson, HCL, Honeywell, Tata Communications,


What is ahu ? Working principal.

0 Answers   Sodexo,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)