generaly all power generating devices is expressed in KVA
or MVA then why power ststion is expressed in MW
Answer Posted / anubis
KVA or MVA is used to measure apparent power. MW is used
for real power. Since the resistance and reactance for a
generating device is known, the apparent power can be
calculated. For the power station the apparent power will
not only depend upon the internal impedence of the station,
and the wies, but also upon the grid. This is not a fixed
number and varies with conditions, thus making it
impossible to judge. Thus it is safer to just give the real
power and then calculate th apparent power depending upon
the load used.
| Is This Answer Correct ? | 16 Yes | 1 No |
Post New Answer View All Answers
if the load is 80 amp for main fuse and 100 amp for breaker so how can we calculate the cable size (cooper ) .
How good are you in resolving the commercial issues to Employer's advantage?
What is meant by rotor?
why power factor is important?
what the principle of sincroscope?how it works?when it needed?
Define sensitivity?
explanation of mesh bus bars
how to ctrl motor by use of ac or dc drive.plz explain evdintly
difference between Ac and Dc mcb ????
what is the difference between oil surge relay and buchholz relay.
In Designing the rating & accessories of a MCCB how to choose the type of releases..means what is the basis for selecting, thermal magnetic, electromagnetic & microprocessr based releases
hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"
what parameters are should nessary for control technic dc drive(in rolling mills)?
Explain the different regions in frequency response?
by what factor the starting current is used when comparing star and delta connection for motor starting?